Daniel-Sp
2020-11-02 15:14:21
- #1
I do not understand the statement. If the room is ventilated with windows, you ventilate with outside temperature, which is included in the calculation with the NAT. A minimum air exchange of 0.5 x room volume /h is assumed. With a controlled residential ventilation system with heat recovery (WRG), however, you do not ventilate with NAT but with a significantly higher air temperature (depending on the degree of heat recovery). Then, with the same ventilation volume per day, you also have a significantly lower ventilation heat loss. And yes, this is calculated for each room individually, depending on the ventilation concept. Usually, in a single-family home's bathroom, there is only exhaust air, meaning the incoming air volume then has the air temperature of the air-supplying room. The controlled residential ventilation with heat recovery changes not only the total heating load but also the room-specific heating load individually, depending on the function of the room (supply air - exhaust air). And you do not have an increased demand but less heating demand. Unless the windows during window ventilation always remain closed...So, the calculation was made before I decided on the ventilation system, according to the heating engineers' statement, but it is not so important even for the individual room consideration. Rather, about 80% of the additional demand due to ventilation can be taken into account again in the total heating demand because of the heat recovery.
: You mean it does not bring much for the overall room temperature?