denz.
2018-09-24 08:20:33
- #1
Check the attached files. I can't open them (with the phone).
It is grossly non-compliant in several respects but not completely useless. Whenever you think you know every kind of foolish "We've always done it this way" incompetence, a new variant appears.If I interpret this correctly, my grounding is useless.
I would agree with that. We should definitely still be able to correct the ring earth conductor, even if the assembly is already backfilled.I assume in favor of the construction company that the ring earth conductor does not form a closed ring only because the material ran out
It should be round steel with Ø10mm+, but how do I recognize if it is V4A?If it can be proven that a stainless steel wire made of V4A with a diameter of 10 mm was laid, the missing ring closure in the ground can at least still be retrofitted
Is a standard-compliant ring earth conductor type B sufficient, or do I definitely need the equipotential bonding conductor connected to the reinforcement? That would be disproportionate and would lead to the demolition of the building.The missing equipotential bonding conductor and the additional connection to the ring earth conductor required by the standard except at the connection tab can only be improved by demolition at disproportionate costs.
Surely they exist, but do you really feel safe with your family then?Electricians with and without supernatural abilities, for whom a glance at a connection tab is enough to bless grounding systems never seen before in the meter registration without batting an eye, are always found.
Certainly they exist, but do you really feel safe with your family then?
It should be round steel with Ø10mm+, but how do I recognize if it is V4A?
Is a standard-compliant ring earth electrode Type B sufficient, or do I definitely need the FPAL with connection to the reinforcement? That would be disproportionate and would lead to the demolition of the building.
*laugh*
| Similar topics | ||
| 25.04.2016 | Potential equalization? Ring earth or foundation earth... | 28 |
| 30.03.2016 | The thermal envelope of the house | 14 |
| 08.10.2017 | Ringerder, where is the best place to install it? | 10 |
| 26.01.2019 | Proper grounding in steel fiber concrete and black tank | 11 |
| 22.07.2019 | Foundation formwork made of Poroton bricks | 39 |
| 21.06.2022 | Is SAT grounding possible via a 7x2.5mm² cable? | 12 |