3x16A is too little for a normal house. If the heat pump is on and some other things, e.g. in the kitchen, are also running, a 16A fuse trips very quickly. Since the three fuses are your main fuses, the electrician should take another look and check how strong the supply line is. Usually, a 10mm² or 16mm² cable is installed from the house connection to the meter cabinet. These can be protected with 50A or 63A fuses. Since there may be 63A in the house connection, you would have to put 50A in the meter cabinet because of selectivity.