Hi,
I wanted to report back with some practical experience after we’ve been living in the house for 8 months now.
In the summer, I operated the device at the calculated nominal power (lower in the heat). I think it was 7.5V out of a maximum of 10V. So already relatively close to the limit. Noise was audible in some rooms, but not disturbing.
Now in winter, despite humidity recovery, the air is quite dry, about 40%. I also activated the power measurement of my KNX switching actuator and was very shocked by the alleged consumption of 105 W. The actuators don’t necessarily measure very accurately, but a second look at the technical data of the controlled residential ventilation shows that the data provided there for power consumption refer to very low air resistances. So my 105 W could well be realistic. The other thing is that despite heat recovery, cool air is being blown into the house around the clock.
I have now lowered it to 5.5V, which is a bit less than the calculated "reduced" ventilation. And what can I say? At least now in winter, it is more than enough. Power consumption is down to 55W, and the system is no longer audible.
I’m curious about the next summer; hopefully it will still be sufficient then. So far, my and your concerns have certainly been unfounded. Maybe it has to do with our construction method.
It turned out not to be so brilliant to install the device in the attic. Although it is insulated, it is not only insulated from the outside but also from the living space. In any case, it cools down quite a bit over time. Currently, it’s 13 degrees. I believe this also "pre-cools" the supply air to the rooms.