Hello everyone,
I had the heating load for my house calculated. Unfortunately, the result is exactly between two devices... Beforehand, a central controlled residential ventilation system with heat recovery is planned.
Here is the statement from my plumbing specialist:
The calculated heating load is approximately 5.6 kW at -10°C. The air heat pump produces about 5 kW at this time, the remaining 0.6 kW is covered by the heating rod. (The next larger device produces about 7 kW heating capacity at -10°C.)
Your possible hot water withdrawal (continuous output) is approximately 254 liters per hour.
These are technical details and now I wanted to throw these values into the group. What do you think of the statements? I live in the Ruhr area, it does get cold here too, -10°C happens less often, but there have been exceptions with -20°C. Would you agree with this statement or tend rather toward the larger device?
Thank you very much and I hope these details are "sufficient"...
Best regards splitti
I had the heating load for my house calculated. Unfortunately, the result is exactly between two devices... Beforehand, a central controlled residential ventilation system with heat recovery is planned.
Here is the statement from my plumbing specialist:
The calculated heating load is approximately 5.6 kW at -10°C. The air heat pump produces about 5 kW at this time, the remaining 0.6 kW is covered by the heating rod. (The next larger device produces about 7 kW heating capacity at -10°C.)
Your possible hot water withdrawal (continuous output) is approximately 254 liters per hour.
These are technical details and now I wanted to throw these values into the group. What do you think of the statements? I live in the Ruhr area, it does get cold here too, -10°C happens less often, but there have been exceptions with -20°C. Would you agree with this statement or tend rather toward the larger device?
Thank you very much and I hope these details are "sufficient"...
Best regards splitti