Air-water heat pump from Rotex hpsu compact 516 experiences

  • Erstellt am 2020-12-05 09:35:49

Chris1990

2021-01-24 19:46:38
  • #1
What is the disadvantage of an oversized air-water heat pump, specifically with 11 KW?
 

Daniel-Sp

2021-01-24 20:05:17
  • #2
Rapid wear due to cycling of the heat pump, as it cannot dissipate the heat. Inefficient operation.
 

Chris1990

2021-01-25 09:21:12
  • #3

Okay, thanks. Upon inquiry, I was told that 11 KW is too much and according to HLB, 8 KW will be sufficient.
 

tomtom79

2021-01-25 09:44:15
  • #4
Even 8kw is probably too much. And this is from someone with kfw70 and 250m2 living in the northern Black Forest who just came back from shoveling snow.

Find out what the standard outside temperature is for your region.

For example, for us it is -14 degrees.

Then look for an online heating load calculator, roughly enter the values and increase by about 20%. I think you will end up somewhere around 5000-6000kw maximum.

But if you are unsure, invest the 300 euros in a professional heating load calculation.
 

Similar topics
09.06.2015Gas, heat pump, and solar for a single-family house?36
21.10.2019Heat pump with heat pump tariff?37
21.10.2017Heat pump underdimensioned for a 6-family house?12
08.03.2018Is heating load calculation with desired temperatures necessary?14
20.02.2018Heat pump calculation formula based on heating load18
14.09.2018Heating (Heat Pump) Incorrect, heat output too high?14
22.11.2019Feedback on heat pump / offer requested!46
12.01.2021Underfloor heating air-water heat pump. House too warm when the sun shines690
04.02.2020Whom to entrust with the room-wise heating load calculation?46
02.04.2020Heating load calculation 10.3 kW, is a 9.5 kW air-to-water heat pump sufficient?29
05.06.2020Heating load calculation or room heating load26
14.10.2022Air-to-water heat pump sizing in new construction311
10.12.2020Heat pump Knv or IDM air heat pump13
14.12.2020Underfloor heating heat load calculation - simply explained?26
20.01.2021Air-to-water heat pump consumption at 30 kWh per day52
08.10.2021Air-water heat pump combined with underfloor heating does not work properly65
15.02.2022Is the surcharge for an air-to-water heat pump justified compared to gas?32
21.06.2022Renovation of heating system for existing property - condensing boiler/air-water heat pump/DHW heat pump25

Oben