But shouldn't it be connected to 230V with a ceiling height of 2.50 m?
 

Smody67

2014-02-11 23:45:51
  • #2
No, not directly in the shower! No 230V!
 

Elektro1

2014-02-13 09:01:47
  • #3


That is not entirely correct:
The installation zone must be observed.
Zone 1 extends from the floor edge up to 2.25 m in height, but at least up to the corresponding water outlet (i.e. shower head).

From Wikipedia:


Area
Construction of low-voltage systems


Title
Requirements for workplaces, rooms and systems of special types


Short description:
Rooms with bathtub or shower


Last edition
2008-10


ISO





Installation zones in the bathroom

In living spaces, rooms with a bathtub or shower count as dry rooms, although moisture occurs in these rooms. Due to the moisture, there is a particular hazard in these rooms because moisture significantly reduces the human body resistance, and in conjunction with earth potential, even small touch voltages can cause dangerous currents to flow through the human body.
Electrical installations in these rooms should be arranged so that hazards due to electric currents are excluded. The detailed requirements for installation are specified in the DIN standard DIN VDE 0100-701:2008-10.
Different protection zones or protection areas are distinguished:


    [*]Protection area 0: Protection area 0 defines the interior of a bathtub or shower with a tub. For showers without a tub (floor-level showers), there is no protection area 0. A radius of 120 cm around the shower head applies as protection area 1.
    [*]Protection area 1: Protection area 1 extends above protection area 0 up to a height of at least 2.25 m; if the water connection is higher (e.g., in showers), then up to that height above the floor and applies to areas above bathtubs or showers as well as the area beneath the bathtub or shower up to the installation platform.
    [*]Protection area 2: Protection area 2 applies to areas extending 60 cm in front of bathtubs or showers that are within arm’s reach. On the wall sides, the area extends up to a height of at least 2.25 m from the top edge of the floor. At shower entrances, this is a circle with the shower wall as the center (string length). The requirements of protection area 1 also apply. Additionally, installation of lights and connection of washing machines is allowed. Sockets and switches are not permitted.

In protection area 0, devices with a protection rating of at least IPX7 are permitted; in protection areas 1 and 2, at least IPX4. Installation devices such as sockets, junction boxes, etc. are not permitted in protection area 0. Consumables in protection area 0 may only be operated if their operating voltage does not exceed 12 V AC or 30 V DC (the supply transformer must be located outside protection area 1), these must be permanently connected and approved by the manufacturer for this purpose (e.g., bathtub heater).
In protection area 1, electrical consumables are only allowed if they are permanently connected water heaters, whirlpool and wastewater pumps, or exhaust devices. Other consumables or installation devices are permitted if their operating voltage does not exceed 25 V AC or 60 V DC. Again, the power sources for supply must be installed outside protection areas 0 or 1.
Cables and lines must be routed to the corresponding devices from the back or from above. Only cables and lines supplying the devices located there may be laid within protection areas 0, 1, and 2. The protection area also extends 6 cm into the wall and therefore, besides the effects on apparent wiring within the bathroom, requires that a mineral residual wall thickness of at least 6 cm must be observed for cables in adjoining rooms, as otherwise these would be considered located within the corresponding protection area and thus may not be installed there.
To protect residents from dangerous body currents, circuits in these rooms must be equipped with a protective conductor and a residual current device (RCD) with a tripping current of no more than 30 mA.
 

Similar topics
19.10.2008Bathtub vs Shower11
28.02.2013Heat demand calculation according to DIN 1283112
24.03.2014Heating proof: Heat load calculation according to DIN 12831 or DIN 4708?10
10.09.2015DIN 4109 Noise - What is to be considered?13
28.11.2016Is sound insulation according to DIN standard 4109 relevant for building permits?16
17.05.2016Shower buffer storage15
09.11.2018Is installation of surge protection according to DIN VDE 0100-443/543 mandatory?15
18.10.2018Construction costs for terraces, etc. in cost estimation according to DIN 2719
14.05.2020Sound insulation VDI Guideline 4100 & DIN 4109 in prefabricated house construction49
24.11.2020Heating load calculation & layout plan DIN: Is a new calculation necessary?41
23.02.2023Consultation: New bathroom, 5.9 sqm with bathtub48
12.01.2021Bathroom ceiling moisture + inadequate insulation44
29.06.2021Electrical Installation New Single-Family House - Evaluation and Suggestions29
27.06.2023Is sound insulation according to DIN 4109-1 sufficient for a mid-terrace house?19
15.12.2022Planning guest WC in new construction - How big should it be? (DIN?)107
27.12.2022Door DIN left or right – are both possible?17
07.11.2024Is window planning mandatory according to DIN 5034-2021-08?13
20.11.2024Is staircase DIN 18065 mandatory or not?82
14.02.2025The planner does not perform any calculations according to DIN 27660
29.08.2025Terrace without slope - From which DIN / regulation?14

Oben