Low humidity room climate (25%)

  • Erstellt am 2020-03-25 22:10:58

gnika77

2020-03-29 13:34:22
  • #1
Unfortunately, yes. And my condolences for this uncomfortable heating system from my side as well. There are two causes for the dry air with this type of heating system:

1. The installed cross-counterflow heat exchanger only recovers heat from the exhaust air. The humidity in the exhaust air is completely transported outside. Since the absolute humidity of the supply air is much lower in cold outdoor air, the relative humidity inside drops to a very unpleasant level. As a remedy, one can retrofit an enthalpy or rotary heat exchanger instead of the cross heat exchanger. This also recovers the humidity from the exhaust air. This would increase the indoor humidity. Unfortunately, the system manufacturer must offer such a heat exchanger.

2. The second cause is the required high volume flow to cover the heating demand, since the heat capacity of air is low. That means the colder it is outside, the lower the humidity of the supply air, which worsens the already higher required volume flows in cold conditions. To reduce the problem, the required volume flow must be reduced. To do this, one can:
- reduce the heating load by improving the insulation of the house (for example, the top floor ceiling) or lower the indoor temperatures
- partly cover the heating load with an additional heater, e.g., split air conditioning, which keeps the humidity indoors so the primary heating system supplies less outdoor air
- increase the supply air temperature. This reduces the amount of supply air needed to cover the heating load and thus dries the house less. Unfortunately, this has the disadvantage that the already poor efficiency of the heating system decreases further.

Fixing the above causes will reduce the problem but not completely solve it. IMHO, the ultimate solution is a humidification coil in the heating supply air. That costs a bit of money. But then dry air should be a thing of the past. Google for example Hygrobox Helios or simply air humidifier ventilation. A pleasant climate should be worth €5,000 to you. Maybe the home builder will consider a goodwill contribution to solve the problem. After all, they sold you this uncomfortable heating system without properly informing you about it.

Regards, Nika
 

guckuck2

2020-03-29 17:48:44
  • #2
Comfort climate heating. One should probably show this to a lawyer to see if there is a defect here. At 25% rH, there can hardly be any talk of comfort anymore. I would certainly laugh heartily if this marketing crap ever had consequences. All this talk of climate walls, etc., is barely bearable anymore.
 

Lumpi_LE

2020-03-29 19:59:14
  • #3
Something like that is great but has a very high power consumption, which must be taken into account.
 

Bookstar

2020-03-29 20:11:44
  • #4
Just checked, we have 26.3 degrees in the dining room with a humidity of 31%.

Thanks to the enthalpy exchanger in the ventilation, the values are already pretty good. We are very satisfied.
 

gnika77

2020-03-29 20:14:20
  • #5
Well, sometimes you have to fight fire with fire ops:
 

Müllerin

2020-03-29 20:16:23
  • #6
26° wow... We also often had it too warm at the beginning when we first had to adjust the heating. What never bothered me at home, but then I was freezing everywhere else, which was not so nice. By now, I think we have about 22° in the living room.
 

Similar topics
09.06.2022decentralized ventilation - various manufacturers39
10.05.2014Settlement at 85% humidity14
06.11.2018New construction 2014: Problems with high humidity in the basement15
03.10.2016Exhaust air and supply air one above the other?22
27.01.2017Exhaust air vs. recirculated air in a controlled residential ventilation system32
13.02.2017Number of supply and exhaust airflows in residential ventilation11
24.03.2017Is the ventilation system connected incorrectly?13
20.04.2017Controlled residential ventilation: place supply air in bedrooms in the wall.23
05.05.2017Central Controlled Residential Ventilation: Supply and Exhaust Air, Door Bottom Gap30
27.02.2018Too high humidity in the apartment. 60-70% in winter33
09.01.2018Exhaust air in the bedroom - supply air in the storage room24
18.03.2024Attic problem. High humidity - Controlled residential ventilation?39
06.04.2023Experience ventilation roller shutter box: Aereco Zuroh 10015
17.02.2020Open kitchen: exhaust or recirculation in controlled residential ventilation & KfW5540
15.10.2020Controlled residential ventilation: positioning of supply and exhaust air in my designs44
27.02.2021Controlled residential ventilation + fireplace + kitchen exhaust, does it work?56
21.11.2020Humidity 60% Masonry damp23
23.06.2021Controlled residential ventilation - Planning the positions for supply air / exhaust air60
02.06.2021Controlled residential ventilation supply air in the living area near the sofa19

Oben