Laying carport electrical wiring

  • Erstellt am 2016-06-19 12:20:46

Payday

2016-06-19 12:20:46
  • #1
moin

in 3 weeks our carport will finally arrive, after we had to wait forever for the paving. I am therefore currently planning our electrical installation in the carport.

Prepared by our electrician:

5x 2.5mm² cables secured with RCD and 16A in the fuse box in the house
5x 4mm² cables, secured through missing fuses in the house, pre-connected for 400 volt socket (electric car)

Both cable ends were already laid to the correct place in the shed of the carport during the paving work.

I will do the installation myself. As a graduate mechanical engineer with training in pipeline construction, I consider myself qualified enough to carry out such work. Because the entire line also has its own fuse, I can easily turn off the electricity for this job (+ test with a multimeter ...)

For the switch program I have chosen Busch Jäger Ocean in blue. IP 44 for covered outdoor areas. I will buy 1x 50 meters cable 5x2.5mm² so that I can connect everything. I wanted to use 5 cores because this way I can loop all 5 wires from the house everywhere (although only 3 are connected) and also only need 1 cable to switch e.g. lamps, while the socket at the switch permanently gets power. I wanted to set up 3 lamp circuits, 1x carport area, 1x shed and 1x covered terrace (table lighting). Each circuit should have at least 2-3 sockets. The carport lighting will have a two-way switch from 2 points and 1x motion sensor.

I wanted to run the cables through Ø20 electrical conduit (rigid conduit), fix the conduits to the carport with quick clamps (OBO Bettermann). I am not yet sure whether I can get the cable directly from the empty conduit into the socket line via an M20 cable gland or similar.

The 5x4mm² cable I will only lay to a distribution box. If I really need the cable, I will leave that to an electrician.

Questions:

- Does 5x 2.5 make sense or are 4 or even 3x 2.5 enough? 2.5mm² is required for 16A, right?!
- Is the Ø20 conduit sufficient or better 25 conduit? I thought the 1x 5-core cable would offer enough options (5x2.5mm² cable has a diameter of 13mm)
- Suggestions for improvement?
 

Sebastian79

2016-06-19 21:22:41
  • #2
I thought you can handle that with your degree program

What do you want to do with a 4mm2 cable? Completely unnecessary and exaggerated...
For 16A sockets, 1.5 cables are sufficient.

I would take M25 and suggestions for improvement? Get someone who knows about it and help him - but if it already fails there and an internet forum is asked, then I would leave it.
 

andimann

2016-06-20 13:00:43
  • #3
Hello

he doesn't want the 5*4mm^2 for the 16 A but for the 32 A connection for the car. That makes sense...

Although, if there ever will be electric cars with usable ranges (>750 km) and charging times (<15 min), even the 32 A is just a drop in the bucket. Even the 32 A connection needs easily 10 hours to charge a 120 kWh battery. That really is the lower limit of what’s useful. Actually, you would need 400 V and 500-1000 amps. But that really is no longer for household use!

Back to the subject:

I will also lay it (have it laid). And depending on the cable lengths, it’s not entirely wrong to increase the cross-sections a bit; if there really is a socket after 50 m, with a tight cross-section and high power demand, it can lead to the current going up and the fuse constantly blowing. Such a situation annoyed me terribly back in my community service. When working with the high-pressure cleaner in the outdoor facilities, someone always had to hold the fuses because they wanted to trip every 2 minutes.

In short, I consider the 5*4 mm^2 and 5*2.5 mm^2 absolutely sensible.

The "thick cable" already has a diameter of easily 15 mm, so I might also take a 25 pipe.

Make sure that the pipe is approved for outdoor use, so it doesn’t crumble after three years due to UV radiation.

Best regards,

Andreas
 

Sebastian79

2016-06-20 13:06:29
  • #4
For 32A, 2 cross-sections of 5 are planned, not 4...
 

andimann

2016-06-20 13:29:49
  • #5
Hi,


nope, you may load 2.5mm² cross-sections with 20-25 A, no more.
for 4mm² cross-sections, it ends at 27-34 Amps. In other words, if things go really badly, strictly speaking you even need 6mm² for the 32 A socket...


Best regards,

Andreas
 

Sebastian79

2016-06-20 13:41:52
  • #6
Dirt - you are, of course, right... Sorry!
 

Similar topics
16.07.2015Cable for outdoor lamp too short11
24.12.2015Electrical planning - sockets88
13.04.2016Electrical planning: Where to install sockets, LED and LAN outlets?19
10.09.2016Empty conduit from the supply room to the attic 50mm - sufficient14
21.03.2019How many power outlets are behind the TV?78
10.04.2017New construction preparation for future experiences16
20.02.2017Sockets or power strips19
15.08.2017Sockets directly under light switches? Pros, cons?17
12.09.2019Electricity in garage: fuse box, circuit, sockets21
18.02.2020What height should the sockets be on the TV wall?11
11.04.2021Plan a conduit for Telekom?21
04.08.2019Sockets: Always prepare sets of 5? What is the best way?25
05.03.2020Carport with massive shed30
06.06.2020Pull the cable through the conduit20
01.09.2020Which conduit for LAN cable?32
18.09.2020CAT cable in the utility room - not crimped?45
03.06.2022Floor plan: 150 sqm single-family house + granny flat - carport / garage + shed / workshop45
27.12.2022Wiring sockets, switches30
09.07.2023Electrician Cost Estimate - New Installation22

Oben