I wanted to change that and then there was only one point left .... Here again something I wanted to include, a quote from ElektroPraktiker about VDE 0100-701 cables in damp rooms
Preferably, installation from the back should be applied in zone 1. Cables and wiring intended for the supply of other roomsCables and wiring intended for the supply of operating and consumer devices in other rooms must be embedded at a depth of at least 6 cm (remaining wall thickness), measured from the bathroom wall surface (Figure ➓). If this condition is not met, such cable and wiring systems may still be installed inside rooms with bathtubs or showers if one of the following conditions is fulfilled the circuits are protected with additional protection by residual current devices (RCDs) with a rated residual operating current I ΔN ≤ 30 mA and equipped with a continuously connected protective conductor. • The circuits are protected by low voltage using SELV or PELV or by protective separation