Is an electrical cable allowed under the shower?

  • Erstellt am 2019-01-03 23:14:07

world-e

2019-01-04 14:17:09
  • #1
In my opinion, it's not totally irrelevant. Just google "VDE 0100-701 Restwanddicke". Cables from other rooms may only be installed in the wall if a remaining wall thickness of 6cm is maintained. Unless they are extra-low voltage or they are grounded and connected via an RCD, which should be the case for an outdoor lamp.
 

blaupuma

2019-01-04 17:05:19
  • #2
I also believe it is Zone 0 and you must have a distance of 5 or 6 cm. I now have maybe 3 cm.
 

Knöpfchen

2019-01-04 18:10:20
  • #3
If the slots are very deep, they should be sealed again with a special insulating mortar. This was recently demanded by an expert on a construction site.
 

blaupuma

2019-01-04 18:37:12
  • #4
Slots are standard
 

Bookstar

2019-01-04 18:53:39
  • #5
At least 6 cm of screed will be applied there. Where is the problem?
 

blaupuma

2019-01-04 19:30:32
  • #6


It’s about the shower wall.

There will be 1.5 cm of plaster plus tile adhesive plus tile on it.
 