Heating screed with device vs. with heat pump: costs?

  • Erstellt am 2022-09-14 22:04:47

Sandra.M85

2022-09-15 13:51:54
  • #1


Above, a demand of about 6300 kWh was stated for my project, where does the large difference come from?
 

WilderSueden

2022-09-15 14:15:21
  • #2
How high is your screed heated? We once had a big discussion here about whether it is really necessary to heat the screed above 50 degrees when, in practice, the flow temperature is only at 30 degrees. I suspect this could be where the difference lies. However, I am also unsure because I don't yet know our planned heating program.

The calculation above is by the way a rough estimate assuming continuous full load at 19 kW. But since the temperature is increased and decreased gradually, I would rather not assume permanent full load.

edit:
I just quickly googled and found a rule of thumb of 20 kWh/sqm. That would then be about 2600 kWh for 130 sqm. Can someone confirm this who has already completed their screed?
 

Mahri23

2022-09-15 14:42:54
  • #3
we also have 130 sqm, but it wasn't that much. Since I couldn't check the meter readings, I would guess 1000 to 1500 kWh, but it definitely wasn't more. As I said, in Aug.20 and it was nice and warm. The screed "almost" dried by itself then.
 

i_b_n_a_n

2022-09-15 15:53:25
  • #4
In our new office, the landlord spoke of a 50° heating temperature. I believe it is also (or exactly?) about relieving stress from the screed...
 

WilderSueden

2022-09-15 16:19:16
  • #5
Yes exactly, it's about the tensions. But I remember a longer thread in which it was discussed whether 50 degrees are really necessary when the heating is designed for a flow temperature of 28-30 degrees. Since you only ever adjust in small steps up and down, a 20-degree difference then means a few more days and precisely the hottest ones. But I can't find the thread quickly.
 

SaniererNRW123

2022-09-16 08:31:56
  • #6
Yep. There are two different types of heating: 1. Functional heating 2. Drying / surface-ready heating Easier than writing it myself: Although functional heating is usually still specified at +/- 50 degrees, it has become common not to go that high anymore, since normally the maximum flow temperature is around 30 degrees and the delta to 50 degrees is no longer needed. How long and how intensely to heat is specified by the screed layer.
 

Similar topics
29.01.2014Cost saving/basement/affordable tiles/sealed screed?13
04.04.2016Drywall boards mold?57
13.04.2017Screed with gold sand17
28.04.2016Order screed - plaster14
27.05.2016Plastic fittings/water pipes and insulating underfloor heating beneath screed?40
29.07.2018Perimeter insulation under the floor slab and still XPS under the screed?28
31.10.2016Heating the screed with the utility provider?!12
29.11.2016Front door only burglary protection / better materials - plaster, screed?10
02.02.2017Is ventilation/drying after installing screed/interior plaster sensible?15
05.08.2017Screed necessary? Unfinished but insulated attic23
11.09.2017Raise the planned click vinyl flooring or increase the screed?12
24.07.2018House 1930s reddish screed and linoleum12
06.11.2018Recess in the screed 5 cm high - How is it done?10
07.05.2020Cracks in the screed. Problematic?25
28.08.2020Urine on wall / on and possibly under screed16
19.03.2021Floor insulation not glued/sealed to the screed27
07.06.2021Installation of heat pump/heating - before or after screed16
03.12.2021Heating phase, screed, window position20
16.03.2023Lowering the supply temperature in underfloor heating more complex than expected?70

Oben