Hello forum,
the required minimum thickness of the screed is regulated in
DIN 18560, Part 2, "Screeds and heated screeds on insulation layers."
For an expected load in residential rooms of 2.00 kN/m², table 1 requires the following values for cement screeds:
Minimum thickness >45 mm
Minimum flexural tensile strength F4
Therefore, the original floor construction with 65 mm is completely sufficient.
When properly executed, experience shows that there are no problems with the chosen construction.
In this context, the installation of the thermal insulation and the ventilation pipes should be carried out as carefully as possible to ensure load transfer. Attention should be paid to laying with as few cavities as possible.
Best regards
Kristof