Hello everyone,
I’m trying to shed a little light on the matter. 1mm² has not been available for a long time, not even as a flat cable [Stegleitung]. Basically, the cable cross-section is designed according to the upstream fuse:
So you want to be able to draw 16A from a socket. By the way, that is the maximum current for conventional [Schukosteckdosen]. To ensure 16A, I have to calculate the cable cross-section based on the length of the cable (loop impedance). So a 3x1.5mm² cable can be laid a maximum of 17m if it is to be loaded with 16A. Either you take a smaller fuse, for example 10A, then you get about 23m, but then you only have a max of 10A at the socket. The next option is to increase the cross-section to 2.5mm². This then allows a maximum length of 25m.
So you cannot generally say that 1.5mm² is sufficient. That it is the minimum cable cross-section for flush-mounted house installation becomes clear when the resourceful DIYer tries to buy [NYM Leitung] at the hardware store.
That the stove should therefore be connected with 2.5mm², since usually a 20A fuse is also recommended by the manufacturer, now becomes clear. But here too, be careful with the cable length. Also note here: new ovens are usually delivered with a normal [Schukostecker]. In this case, only the oven should be connected to this fuse (socket). The same applies to dishwashers.
And please remember, all circuits that lie within the non-professional area must have [FI] protection since mid-2007. This also applies to DIYers!
It is best to have a registered craftsman take another look at the whole matter.
This is only meant to be a very brief and rough overview! The matter is much more complex.
Regards
JonnY