Allthewayup
2024-03-19 20:15:53
- #1
Thank you So it is urgent for you. Soil survey available? If yes, soil permeability value? Size of the excavation pit? Distance to neighboring buildings? Approval for the lowering obtained from the local water authority? 1.7m is already a lot but not impossible with well-permeable soil. I would rely on 2 extraction wells going down to 4.50m depth. The discharge into the sewer (liters per second) must be clarified and you must know what quantities to expect when pumping! Especially for the dimensioning of the system. Someone must monitor the system (24/7). If it fails overnight, pumping for 2 days is wasted and if the basement walls are already standing and there is too little load on the floor slab, it could worst case scenario float up. Are there photos of the status quo? *Edit: 470m??? Is it uphill/downhill there? Even horizontally that means an immense pumping capacity. Are you aware of the costs of this operation?