Does the temporary construction power connection need to be inspected monthly by an electrician?

  • Erstellt am 2017-11-08 06:37:34

Bau-Schmidt

2017-11-08 19:20:18
  • #1
Where does it say monthly? It says it could look like this.

Recurrent tests

The frequency of recurrent tests is based on the specifications in the risk assessment, the scope according to the specifications in VDE 0105-100.


Note:
Setting test intervals could look for example like this:


Daily - pressing the test button of the residual current device by the user
Monthly - metrological testing of the residual current device by a qualified person
Semi-annually - measurement of insulation resistances and inspection of protective conductor connections by a qualified person


Every electrical installation must be tested by a qualified electrician before commissioning, after modification and after repair, as well as at appropriate intervals (§ 5 BGV A3 or § 5 GUV-V A3). The tests must be documented.

Because testing a construction site power distributor serves occupational safety and protection against electrical accidents. The following standards and regulations must be observed for testing construction site power distributors:


    [*]VDE 0100-704
    [*] VDE 0100-600
    [*] VDE 0105-100
    [*] BGI 608
    [*] VDE 0660-501
 

Kaspatoo

2017-11-10 20:36:30
  • #2
Should you pay for that? I wouldn't do it, the [GÜ] should pay, since construction electricity is probably contractually defined on the [GÜ]'s side, right?
 

ONeill

2017-11-10 21:17:59
  • #3
On our site, construction power had to be provided on site. I believe this is often the case as well.
 

haydee

2017-11-10 22:12:20
  • #4
Construction site electricity provided by the client According to the main contractor, it has recently become mandatory to pay monthly (a well-known electrician says otherwise) The charged time is outrageous. The main contractor agrees. They are not the only ones. The construction site electricity box was originally included in the civil engineer's offer. They are no longer allowed to just set it up. At some point, there was a call asking if xy may set up the construction site electricity box - Yes. We thought we would pay for the setup and roughly the same amount for the rental. Next week, I'll have to keep a close eye on the electrician. This can't continue like this. Next time, he has to make an appointment and I will stand next to him,
 

Similar topics
02.01.2015No construction power box, take electricity from the neighbor18
11.03.2016Expensive developer contract?20
18.11.2016Electrician's invoice after 2.5 years - What are my rights?18
12.05.2017Is an advance payment to an electrician lawful?23
11.11.2018Temporary power distributor - buy or rent?11
01.08.2019Trouble with the electrician / tolerance range?!42
20.02.2020What does the electrician do during the shell construction phase?19
23.03.2020Building law: Electrician refuses to continue78
21.07.2021Problem with the electrician - what would you do?78
08.10.2022Requirements for construction power box Construction power distributor12
09.07.2023Electrician Cost Estimate - New Installation22
05.11.2023Maintenance contract for construction site power distributor37

Oben