Dimplex SI8TU ground source heat pump - strange behavior

  • Erstellt am 2021-05-20 17:32:41

Fuchur

2021-05-20 17:32:41
  • #1
Since our photovoltaic system, despite O/W/W orientation, is throttled to 70% daily, I am currently dealing with how to capture these peaks. In the process, I stumbled upon a strange behavior of our heat pump for which I have no explanation so far.

Installed is a Dimplex SI8TU with deep drilling. Commissioning was carried out by the factory service. The performance of the brine circulation pump can be adjusted in steps 1-10 (on the pump itself). During installation, step 1 was set. As a result, this regularly led to temperature spreads of the brine of >9K in winter. The hot water ran at 50°C.

As part of efficiency optimization and elimination of various defects (hydraulic balancing etc.), the hot water temperature was slowly lowered and the brine pump was increased until the spread was about 3-4K, most recently to step 5.5. The COP has increased significantly as a result. Meanwhile, the factory service was here for another matter and looked at the system. He pointed out that the brine pump must be set to step 10, because the heat pump can only work efficiently that way. The more flow, the better. Meanwhile, the heat pump is in summer operation and the cooling function was temporarily on, causing the brine temperatures to rise significantly. Now the heat pump already goes into high-pressure fault at a hot water temperature of 43°C. As a test, I set the brine pump back to step 1 today and promptly the heat pump delivered hot water at 49°C until I switched it off myself.

I always thought the higher the brine temperature, the lower the necessary temperature increase and thus the more powerful the heat pump becomes? That’s what the data sheets show as well. The manual contains the (nonsense) sentence: "The lower the heat source temperature (e.g., outside temperature, brine temperature) the higher the achievable hot water temperature." I had so far considered this a typo/translation error, but it exactly describes the observed behavior. Is this related to the evaporation temperatures of the refrigerant or how can this be explained? If it really is as it is, then the only help is to manually adjust the brine pump in winter and summer.
 

guckuck2

2021-05-31 06:09:32
  • #2
High pressure faults are usually due to a lack of heat removal. Some closed valve? Buffer overheating?



How high is the supply temperature in this case? I assume significantly higher than the storage temperature, the return temperature is quite close to the supply temperature?
 

T_im_Norden

2021-05-31 06:41:51
  • #3
The heat pump cannot remove the heat, how large is the heat exchanger in your hot water storage?
Possibly there is a filter somewhere that is clogging up.
 

driver55

2021-05-31 11:11:28
  • #4

But the heat pump is not running in Germany.

And "brine temperatures have risen significantly"? Never!

What brine temperatures prevail currently after 10 minutes of heat pump operation?
 

Fuchur

2021-05-31 16:17:39
  • #5

Yes, I am aware of that. The first measure was also to turn the domestic hot water circulation pump up to the maximum. Otherwise, it goes directly into the storage tank (300L) from there. The technician also told me that >50°C is not possible due to "losses at the heat exchangers and the distance heat pump-storage [approx. 2-3m]".

I would have to check the exact values, but yes, from memory the flow is somewhat higher.


According to the data sheet 3.5m², Dimplex WWSP335. I don’t see any serviceable filter units anywhere.

I can only read the values that are displayed to me. At the end of the heating season, the source input was about 4-5°C after 1 hour of operation, currently it is 9.x°C. It is a borehole with 130m depth.
 

Fuchur

2021-06-01 20:51:24
  • #6


So, for today's 2 hot water preparations, I had the data logged. The first cycle was during the "shower phase" in the morning, hence the fluctuations in water temperature with a target value of 42°C. The second cycle was triggered at noon by photovoltaic surplus, target temperature 48°C. Hot water circulation pump at full power, brine circulation pump stage 1.0 of 10.0.

Why the brine temperature is so high again after such a short time, I don’t know. We live on a mountain, drilling into bare rock, groundwater extremely unlikely. But you can clearly see that the source return temperature rises, indicating the temperature difference decreases as the water temperature rises.

 

Similar topics
25.01.2016Hot water only with heat pump?10
21.06.2016Heat pump with photovoltaics vs gas and solar thermal52
10.10.2017New photovoltaic system with storage in single-family house - experiences39
03.01.2017Preparation for photovoltaic or solar thermal with air-water heat pump18
22.05.2017New build bungalow - air-water heat pump, photovoltaic and solar thermal?17
07.05.2020Collaboration of air-water heat pump, photovoltaic system and storage38
05.12.2020Gas with solar thermal? Or heat pump with photovoltaics? Consultation149
05.05.2020Photovoltaic system + storage with or without cloud tariff13
08.05.2020Heat pump + photovoltaic system with or without storage11
06.10.2021Photovoltaic system / heat pump, do you have 2 meters?55
07.11.2021Newly built single-family house - gas or air heat pump + photovoltaics + storage?169
03.01.2022Electricity meter for heat pump in combination with BAFA and photovoltaic22
25.03.2022Switching from gas to solar / photovoltaic with / without heat pump31
28.03.2022Photovoltaics are coming up - Options: 19 kWp, 25 kWp, 30 kWp, Storage?30
15.11.2022Tecalor 8.5 Air-Water Heat Pump: Warm water - not hot in the morning21
15.12.2022Electricity consumption heat pump experiences?22
20.09.2023Convert hot water from solar thermal system to photovoltaic system?12
18.09.2023Optimization of heat pump LWD 70A with photovoltaics16
17.10.2023Evaluation of photovoltaic system offer with storage78
04.03.2024Costs for heat pump and photovoltaic in 2024 in small old buildings20

Oben