Blower Door Test 1.7 with two hints

  • Erstellt am 2019-12-17 19:49:06

Adunoh1983

2019-12-17 19:49:06
  • #1
Hello, we are having a house built Kfw 40 timber frame house without a ventilation system.... Today I received the data from the blower door test.

Result 1.7 With two indications of air infiltration points

Leaky at all inspection openings of the roller shutters due to the construction

And a hole in the vapor barrier foil of the ceiling slab possible moisture damage in the insulation layer.

Test is passed do I have to accept it as is?

I am an absolute layman and grateful for any tips
 

boxandroof

2019-12-17 19:53:20
  • #2
I also had modest results and caused drama. You may have to accept the passed test, but all construction defects should be remedied. Especially with the vapor barrier. How far along is the construction, interior cladding already on it? Perform a second test during or after defect remediation.
 

Adunoh1983

2019-12-17 19:56:06
  • #3
Hey no ventilation system

Yes everything is already clad from the inside... Test was done a month ago but I only received the results now...
 

boxandroof

2019-12-17 19:59:34
  • #4
Was it only clad or plastered over in the meantime?
Have the defects been rectified?
 

Adunoh1983

2019-12-17 20:05:02
  • #5
No, it was already plastered and covered before...

The holes where the electrical cables come from the ceiling for lamps or spots were recorded in photos.

I don’t think anything was fixed...
But I will call the construction company tomorrow...

But they have to fix the recorded issues, right?
 

seat88

2019-12-17 20:05:25
  • #6
Window certainly with window rebate ventilation, right? The result is OK for that. The limit value is 3.0. The mentioned notes, especially in the vapor barrier, cannot be proven anyway, so they are also difficult to fix.
 

Similar topics
11.05.2010Ventilation system in the new building12
09.09.2010Ventilation system in the new building, yes or no?39
12.05.2014KfW 70 without ventilation system107
28.01.2017Costs for ventilation system experiences18
29.02.2012What can be detected in a blower door test, which house values?18
08.07.2012KfW 70 Ventilation / Exhaust System10
01.05.2015Building without a ventilation system using hollow bricks?35
31.07.2013Ventilation system with heat recovery - sense or nonsense?18
01.10.2015BlowerDoor test mandatory for ventilation system and KfW7016
22.09.2016Offer KfW70 house - KfW55 house already with additional controlled residential ventilation - Is KfW70 too airtight?12
25.01.2017Blower Door Test for KfW 70 according to the 2012 standard?15
21.04.2019Floor plan planning shortly before submitting the building application1420
07.02.2020Blower Door Test - Meaning of the Result35
28.05.2018Windows & window size: what to choose? Double-leaf windows?46
08.10.2020Is the general contractor payment plan acceptable? Thanks for tips68
31.10.2018Concern about vapor barrier - air from ceiling outlet12
06.09.2019Is it no longer allowed to open the windows with a ventilation system?15
27.11.2020Myth?! "Breathing Walls" What is the truth?54
09.07.2021Building according to the Energy Saving Ordinance 2016 or KfW5543
21.02.2022Energetic renovation of old buildings - is a ventilation system necessary or not?12

Oben