Here Energy Saving Ordinance 2016 without ventilation, the house has an airtight envelope but everything without foil, and of course had to pass the blower door test.
Basement solid construction with Poroton brick T12 36cm,
Ground floor + attic completely wooden house with approx. 34.8-38.8cm exterior walls U-value 0.13-0.15 W/m²K
+ exterior plaster
+ 6cm wood fiberboard
+ 6/20 and 6/24 duo louvered timber studs with 20-24cm blown-in insulation
+ 1.5cm OSB
+ 6cm installation layer with wood fiber insulation board
+ 1.5cm OSB (joints glued with airtight tape = airtight envelope)
+ 1.3cm drywall
+ painter’s fleece + interior paint
Roof overall with
+ tiles
+ 3cm battens
+ 3cm counter battens
+ 1.6cm diffusion-open wood fiberboard
+ 8/24cm solid structural timber rafters with 24cm blown-in insulation
+ 1.2cm OSB board, joints glued
+ 3cm battens
+ 1.3cm drywall
The temperatures were absolutely comfortable during the first hot weeks. Maximum room temperature in the attic around 24°C with 35°C outside.
Air-water heat pump then of course only produces hot water.
Here temperature comparison weather station on the roof outside, and on the same day in the ground floor living area. It had already been hot for a few days. At night just always ventilate well.