Bathroom ceiling moisture + inadequate insulation

  • Erstellt am 2021-01-11 08:46:27

Nida35a

2021-01-12 09:04:29
  • #1
The ceiling was/has been opened for repair and left open for inspection, the warm air from the living area rises and condenses on the underlay membrane, which only stops once insulation and foil close the hole again, that's why it is now soaking wet
 

Alessandro

2021-01-12 09:07:25
  • #2
Also put a hygrometer in the bathroom yourself to get a feel for the humidity.
Constantly above 70% poses a risk of mold.
 

WingVII

2021-01-12 09:19:22
  • #3
However, the builder already made a mistake beforehand. Because they are indirectly obligated (building according to the state/rules of technology) to create a ventilation concept according to DIN 1946-6. If they did not explicitly inform the buyer that this is missing, they can be held liable for later damages. It cannot be expected of the resident in new buildings to ventilate sufficiently themselves. A ventilation concept would have shown that a decentralized ventilation or a controlled residential ventilation is necessary. Even window rebate ventilators are not sufficient here.
 