I believe most people here have not understood the Proxon air heating system. It is not an air-to-air heat pump! It is a normal ventilation system with heat recovery through a cross-flow heat exchanger, which transfers up to 85% of the heat from the exhaust air to the supply air. The reheating (essentially the loss compensation) is provided by small electric heating elements in the ceiling outlets of the supply air in the rooms. This allows each room to be individually, quickly, and easily tempered. The necessary electricity should ideally be supplied by a photovoltaic system. A heat pump is not used here at all.
The statement that air is a poor medium for heat transfer cannot simply be left like that in this case either. Yes, air has a lower specific heat capacity than, for example, water, meaning I have to "move" more air than water to transport 1W. The ventilation system does this anyway, which is why air heat transport is calculated in cubic meters per hour and not in liters per hour. Secondly, the elements heat where the heat is needed, so there are virtually no transport losses.
The idea that a radiator or underfloor heating heats the room better is also nonsense. If a room requires 100W/h of heat, I have to bring these 100W there. No matter how.
The fact is, I feel the warm air directly on my body. The system therefore responds much faster than a water-based system.
A radiator first has to get warm itself and then transfer the heat from the heating water to the room air and surrounding surfaces for me to feel it, so it is slower than an air heating system.
Underfloor heating even more so because there is no convection component at all, and the entire screed must also be heated. Additionally, both water-based heating systems stir up dust in the house, whereas the air heating system filters it out.
The only heat pump part of the Proxon system is in the drinking water heating via an (exhaust) air heat pump. This is connected behind the exhaust air duct of the ventilation system. The air that leaves the house and has already transferred 85% of its heat to the fresh air in the cross-flow heat exchanger of the ventilation system has further heat extracted from it in order to use the energy and transfer it to the domestic hot water using heat pump technology. Doing it this way is actually very clever because instead of blowing the exhaust air outside at, for example, 10°C in winter, you also use the last bit of usable energy content.
Similar to a condensing boiler, where the exhaust gases, i.e., essentially the combustion waste product, are cooled down so much by a subsequent heat exchanger that almost all the energy is extracted from them and they cannot even rise up the chimney on their own but have to be actively vented, here another heat exchanger is connected "behind" the ventilation system.
Now you can also understand why Proxon systems often drip. Of course, this should not happen uncontrollably but via the drip water connection!
Warm air can bind more water vapor than cold air. So if I now lead the warm room air, which contains a relatively high amount of water vapor (from cooking, showering, sweating), over the cold incoming fresh air to recover the heat, condensation water MUST inevitably form! Therefore, filters, condensate pans, and condensate drains should be cleaned regularly.
From my point of view, such a system makes a lot of sense because it combines the ventilation system, which is already absolutely necessary today, with an inexpensive heating system, provided the entire system is properly coordinated (e.g., its own photovoltaic system with battery) and balanced.
Because as with a water-based heating system, ventilation/ventilation heating also requires a "hydraulic" balance. All supply air valves must be set appropriately for the room to ensure the exactly matching volumetric flow, just like heating valves. This is done using an electronic vane anemometer with a funnel, which is pushed over the respective connection.