KlaRa
2016-03-11 13:54:31
- #1
Hello Frank. We have already met in one of the other forums here. The bathtub must be placed on the floor slab/concrete ceiling for load transfer! Trying to level the screed, which lies on insulation layers, by grinding or milling is pointless! Because with reduced thickness, the load-bearing capacity of the screed also decreases. So how should one proceed? The solution is simple: First, you need the measurement of how much the screed needs to be notched afterwards. It must be cut out to the necessary extent. This is unproblematic, especially since at least one side adjoins the wall! On the execution date (choose only a cutting technique with good dust extraction!!!), you will commission the sanitary installation company that installed the underfloor heating to turn off the heating and depressurize the system. They must also bring material to inevitably reconnect heating elements cut during the screed removal. The screed section will be cut out, the damaged heating elements reconnected, water refilled in the heating system, and then everything will continue as usual! Floating screeds in residential construction are designed for a vertical surface load of about 150 kg/m². The edge areas are subject to higher stress than the center areas. With a filled bathtub and occupants, 150 kg/m² is quickly exceeded. The screed can (and this is realistic) break under the stress if the bathtub is placed on the "floating screed." The damage scenario mentioned here is real – I can confirm this from my own professional experience. --------------------------- Best regards: KlaRa