Hello,

the last socket is causing strange problems, and I am sure one of you will recognize the error.

It is a surface-mounted double socket in the attic. At the bottom in the fuse box, the fuse for it was installed by the electrician as standard. It is also the right one: when I switch the fuse off, the phase tester does not light up upstairs. When I switch it to green/on, the phase tester lights up clearly in one hole – and very weakly in the other hole. I always thought it only lights up in one hole of the socket?

Well, I have a 3-outlet power strip connected to the socket, whose LED also lights up. As soon as I plug a lamp into the 3-outlet power strip and want to switch it on, the LED of the power strip goes out. The lamp does not light up.

If I plug the lamp directly into the 2-gang surface-mounted socket, it flickers lightly at one-second intervals. Far from lighting properly. It is an LED GU10 bulb inside.

Am I getting insufficient current up to the attic? What could be the cause?

There is power (the LED of the power strip lights up and the bulb at least flickers weakly), so why so little?

I have already rewired the sockets (right blue and left brown, although that should be irrelevant with alternating current anyway), nothing works or the same problem as above.

Is something wired incorrectly in the fuse box, perhaps?

Thanks and many sunny greetings
 

PhiIipp

2022-02-08 10:35:16
  • #2
That sounds like a nasty error in the installation, or you have a faulty appliance in the circuit.
The slight glow of the [Phasenprüfer] in the "other hole" should not happen. There is voltage where it does not belong.
Unfortunately, the [Phasenprüfer] won't help you further here.

If it’s not too much trouble, I would suggest that you switch off all the fuses except the affected one (it’s always annoying with radio alarms and such gadgets) and unplug all appliances on the same circuit from the attic.
After that, try again with the [Phasenprüfer] and socket/lamp and get back to me.
 

danixf

2022-02-08 10:36:35
  • #3
If I were you, I would turn off the fuse immediately and have the electrician come over. He should measure the line. Is it a new building or was the line newly installed? Then I wonder what he measured... It could of course also be a consumer that is defective... My predecessor is right. First disconnect everything and check again, and if the error still persists, make a report.
 

Mycraft

2022-02-08 10:54:13
  • #4
You definitely have a wiring error somewhere, e.g. a broken wire or loose connection. Before it leads to bigger problems -> call an electrician and have the error fixed.
 

annab377

2022-02-08 14:40:53
  • #5
Yes, it is a new building. The cable (3x1.5mm2) runs up the exterior facade to the attic.

He probably didn’t measure anything there because he only installed the fuse. Upstairs in the attic he neither measured nor installed anything. I was the one who first connected the surface-mounted socket to the 3x1.5mm2 cable.

Thanks for your help, then it probably won’t be that easy after all. Hope no cable break / damage.

I will test:
a) measure the cable from the fuse (resistance should be 0 ohms on all three wires)
b) connect a load (lamp) to the fuse instead of the cable and see if it lights normally (if yes, then the problem is probably really after the fuse on the cable).
 

seat88

2022-02-08 14:54:20
  • #6


You connected it? Aha, could the error lie there?
 

Similar topics
07.07.2014LED Recessed Spotlight Positioning Proposal29
31.03.2015LED ceiling spotlights in prefab house construction14
02.10.2016Which LED recessed spotlights / price?14
01.02.2017Conversion to LED Lighting - Financing13
10.07.2017LED instead of halogen spot23
12.09.2019Electricity in garage: fuse box, circuit, sockets21
27.03.2019LED Spots Cost - Can it be that expensive?14
03.11.2019Lighting design with LED spots for hallway13
15.04.2020Connect the fuse box in the construction container14
19.06.2020Is an extra circuit / residual current device really necessary for the office?40
25.07.2021LED strip ascending parallel to the staircase12
03.10.2021Main lighting with LED strips: is it useful?43
21.08.2021Lighting planning - mixture of spots, strips, and lamps13
19.11.2021Stair lighting with LED strip13
07.11.2021What type of cable is needed from the fuse box to the stove connection?13
23.03.2023LED staircase lighting distances for curved stairs21
03.12.2022House connections, block up the fuse box?12
09.07.2023Electrician Cost Estimate - New Installation22
12.03.2025Lighting design for a multi-story apartment with indirect LED lighting50
25.04.2025Mini LED Spots for Terrace Canopy37

Oben