Hello again to everyone,
I wanted to give you an update on this topic. We have now received the expert report, and it raises concerns about two aspects of our electrical installation:
1️⃣ The large cable duct in the exterior wall
2️⃣ Empty conduits on the raw ceiling
I would like to hear your opinions and suggestions regarding this:
✅ Are there actually any problems with fire protection in such an electrical installation?
✅ Which measures would be sensible for the empty conduits to avoid problems with the screed?
Background: The empty conduits run to the large cable duct through a narrow corridor on the first floor and from there to the technical room in the basement. An alternative routing was apparently difficult to realize.
I look forward to your expertise and your suggestions!
Many thanks and best regards!
2. Findings
2.1 Electrical and Smarthome installation
[*]Increased load on power cables compared to standard buildings detected. This is due to the additional wiring for the smarthome system, resulting in more cables distributed throughout the building than usual. Especially in the area of the main cables, numerous cables are bundled, which can cause both space issues and thermal stress. A detailed review of the cable routes is required here to ensure that no overheating or inadequate insulation occurs.
[*]Cable duct with a width of approx. 48 cm and a depth of approx. 18 cm present in the exterior wall. (see photos 1.1 and 1.2)
[*]This design could cause damage to the wall construction as well as to the thermal insulation
[*]Recommendation: Check an alternative cable routing within the interior walls and properly close the open duct with suitable material
[*]Fire protection: All cable ducts must be closed with approved materials according to the applicable fire protection regulations in order to minimize fire risks.
[*]Screed preparation: Due to the multitude of laid cables, air gaps may occur in the screed, which can cause cracks or settlements in the floor. Special care is required here. (see photo 2.1)
2.4 First floor
[*]A cable duct with similar dimensions was also found in the exterior wall on the first floor. It runs vertically along the exterior wall and affects both the structural integrity and the thermal insulation performance of the building. Due to the depth and width of the duct, there is a risk of thermal bridges, which can lead to energy losses and possible moisture damage in the long term. Furthermore, the structural integrity of the load-bearing exterior wall could be impaired due to the weakened structure. It is urgently necessary to check whether an alternative routing of the cables within the interior walls is possible to avoid these negative effects. If this is not possible, suitable measures for proper closure of the duct with structurally appropriate material and a complete restoration of the insulation layer are required. (see photos 5.1 and 5.2)
[*]Recommendation: The cable routing should be optimized to enable better guidance of the installations. Air gaps in the screed are to be avoided. (see photo 6.1)