Hello everyone,
we have some corner windows in our new building. The structural steel columns were placed directly on the masonry by the shell builder, and the window installer then mounted the windows. The window profile was insulated and shuttered on the outside at this point. We generally have a 16cm ETICS. Inside, the steel column is still exposed because we weren't sure yet whether we wanted to clad or paint it.
Now I have noticed that the steel column is relatively cold at the top and bottom. At an outside temperature of 3°C, the wall is about 20.3°C, the window frame 17.4°C, and the column in the middle 14.5°C. But at the bottom, the steel columns show temperatures from 12.4°C to 13.2°C. In the cavity (between the exterior cladding and concrete) it is even 10.7°C. One steel column goes down to the floor and, due to the floor structure, there is a small cavity there, so to speak. For the others, it is, for example, the windowsill.
I have now heard that such steel columns are generally difficult, but is this normal? I have been told now that I should fill the cavity with insulating foam and (insulate and) clad the steel columns.
What do you say? Is this nothing unusual and the suggestion the best thing to do, or was something "forgotten" here and the suggestion is only so that at least something is done? It would be annoying if the column now rusts due to condensation. Especially if I clad it, I won't notice it.
What do you say?
we have some corner windows in our new building. The structural steel columns were placed directly on the masonry by the shell builder, and the window installer then mounted the windows. The window profile was insulated and shuttered on the outside at this point. We generally have a 16cm ETICS. Inside, the steel column is still exposed because we weren't sure yet whether we wanted to clad or paint it.
Now I have noticed that the steel column is relatively cold at the top and bottom. At an outside temperature of 3°C, the wall is about 20.3°C, the window frame 17.4°C, and the column in the middle 14.5°C. But at the bottom, the steel columns show temperatures from 12.4°C to 13.2°C. In the cavity (between the exterior cladding and concrete) it is even 10.7°C. One steel column goes down to the floor and, due to the floor structure, there is a small cavity there, so to speak. For the others, it is, for example, the windowsill.
I have now heard that such steel columns are generally difficult, but is this normal? I have been told now that I should fill the cavity with insulating foam and (insulate and) clad the steel columns.
What do you say? Is this nothing unusual and the suggestion the best thing to do, or was something "forgotten" here and the suggestion is only so that at least something is done? It would be annoying if the column now rusts due to condensation. Especially if I clad it, I won't notice it.
What do you say?