Sockets: Always prepare sets of 5? What is the best way?

  • Erstellt am 2019-07-31 12:52:02

Scorpy

2019-08-01 16:38:48
  • #1
But be careful that the N does not get overloaded with an unsymmetrical load. With 2.5 mm² this is difficult but not impossible.
 

Knöpfchen

2019-08-01 20:13:21
  • #2
Supplying the sockets with three-phase current and then splitting it is absolutely against the VDE regulations. That is TABU! completely unacceptable.
 

M4rvin

2019-08-01 23:44:27
  • #3
Are you sure? What speaks against it? Obviously, one should not overload the neutral, but I hardly think that three heating lamps are connected to all sockets!
 

Scorpy

2019-08-02 10:42:06
  • #4
VDE 0100 Part 520:

The assignment of a common neutral conductor for several main circuits is not permitted. However, single-phase AC circuits consisting of one phase conductor and the neutral conductor may be formed from a three-phase circuit with a neutral conductor, provided that the affiliation of the circuits remains recognizable by their arrangement. This three-phase circuit must be able to be switched off by a switch that simultaneously disconnects all active conductors.
 

Mottenhausen

2019-08-02 14:21:37
  • #5
I don't understand what circumstances would justify, for example, needing a 5-way power strip later at the location of a double socket. Ok, at Christmas, where the tree is. But for such highly temporary emergencies, you just make do with a €10 power strip and put it away afterward.

Generally, I wouldn't know where you would need more than one double socket.

Locations for entertainment etc. are anyway predetermined by the corresponding multimedia sockets, which cannot necessarily be made available preventively in arbitrarily many places if you don't want to invest a fortune in cables.

If there really is a concern about being under-equipped in the future, then I would distribute some additional double sockets in each room and that’s that.
 

11ant

2019-08-02 16:58:06
  • #6
I do - however, I think it is naive to try to prepare today’s equipment for a demand in ten years: by then, there will long have been a bus system according to the KMHNN standard (doesn’t exist yet), and the kids in daycare today (then teenagers) will laugh themselves silly that dad thought it was forward-looking to provide two more 220V AC power ports in reserve from this antique system with separate power/data channels.
 

Similar topics
27.12.2013Help with planning! Where to install the sockets?10
15.01.2014Turnkey construction / self-employed / additional sockets16
24.12.2015Electrical planning - sockets88
13.04.2016Electrical planning: Where to install sockets, LED and LAN outlets?19
15.08.2016Minimum requirements for the number of sockets?11
21.03.2019How many power outlets are behind the TV?78
20.02.2017Sockets or power strips19
15.08.2017Sockets directly under light switches? Pros, cons?17
12.09.2019Electricity in garage: fuse box, circuit, sockets21
18.02.2020What height should the sockets be on the TV wall?11
16.07.2019Sockets and light switches are not connected in parallel22
13.10.2020Planning sockets and burn sites36
01.03.2021Retrofit child safety socket / touch protection22
09.04.2021Switchable sockets / Ideas and tips18
14.02.2022How many power outlets should a kitchen have at minimum?19
27.12.2022Wiring sockets, switches30

Oben