Sizing of our air-to-water heat pump in KFW55 new build semi-detached house 120 sqm

  • Erstellt am 2021-04-05 22:40:32

Stammheimer

2021-04-05 22:40:32
  • #1
Hello,

We are building a KFW 55 duplex house with a developer, 120 sqm + attic with about 15 sqm heated, and we are currently questioning the offer from our developer for the planned air-to-water heat pump.

To receive the BAFA subsidy of 35% for new construction, our developer planned the Nibe F2120-8 + VVMS320 for us. Of course, we applied for the BAFA subsidy back in 2020, the duplex is currently under construction.

The heating load calculation by the energy consultant resulted in 3 kW (temperature -7 degrees). Up to 4 people are supposed to live in the house sometime in the future, so we are also calculating about 0.8 kW for hot water preparation. The duplex will have underfloor heating.

Now we are afraid that the air-to-water heat pump Nibe F2120-8 is totally oversized and possibly does not operate efficiently (keyword cycling, switching on and off, etc.).

We would be very happy if you could share your opinion about our building project and the air-to-water heat pump. We might still have the option to choose a different air-to-water heat pump, but then we would have to forego the BAFA subsidy.

Thank you!
 

Daniel-Sp

2021-04-06 07:54:00
  • #2
The heat pump can only modulate down to 3kW. So "one winter, one heating cycle" is not going to happen. Are the -7°C the NAT? How was the heating load calculated? According to PHPP? According to your information, the heat pump is oversized. Whether it cycles frequently because of this mainly depends on the hydraulics. Cycling usually refers to very frequent compressor starts with run times of just a few minutes and premature termination of the heating cycle due to poor hydraulics. I would not call 3-4 starts per day with run times of 3-4 hours cycling, for example. What options do you then have regarding the choice of heat pump? Are you building with a general contractor or have you awarded the heating trade yourself? Are other heat pump manufacturers also possible? Also pay attention to the hydraulics. No heating buffers, no separation tanks, sufficient flow in the heating circuit. Design of the underfloor heating according to room-specific heating load calculation based on the desired temperature for the individual rooms. Is the handover of all calculations to you contractually agreed upon?
 

Stammheimer

2021-04-06 08:04:42
  • #3


According to DIN EN 12831-1 with a general contractor and basically no choice...
 

Daniel-Sp

2021-04-06 09:55:31
  • #4
Maybe you can at least push through the 2040s, they can throttle down to about 2.3 kW.
 

Daniel-Sp

2021-04-06 09:58:06
  • #5
Then the actual heating load will be even lower thanks to internal and solar gains.
 

Similar topics
07.10.2016BAFA funding tips38
23.09.2017Bafa innovation funding for heat pump possibly too late - what now?15
30.09.2018BAFA funding for air-water heat pumps in new construction - how does it work?30
15.02.2020KFW55 funding + BAFA funding57
20.01.2020New BAFA funding - Air-to-water heat pump with solar thermal39
09.02.2020BAFA - Funding: House contract before application submission?10
03.06.2020KfW 55 + BAFA Funding - Costs and Subsidies24
24.05.2020Heat pump and BAFA - What is true and what is not?24
13.09.2020BAFA funding for heat pump (air-to-water heat pump) when building with a developer25
14.02.2024Bafa funding for heat pumps will be discontinued as of 31.12.2020.510
20.04.2021BAFA funding depends on the form "Confirmation of the Developer"20
03.01.2022Electricity meter for heat pump in combination with BAFA and photovoltaic22
17.12.2024BAFA funding - experiences with payout duration?52
01.08.2023BAFA Funding - What Waiting Time Is Realistic?27
30.06.2023Cancellation of an already confirmed Bafa funding15

Oben