Newbi23
2024-12-02 05:00:58
- #1
Hello everyone,
as already described in another thread, I want to switch to a heat pump at short notice (gas heating acting up for the second time now).
In order to find the right manufacturer/partner at all, I have dealt with the topic of sizing (not so easy, as I have only owned the house for 6 months).
Key points about the house:
- built in 2001
- 150m² living space, of which 40 are in the basement (half window) and currently do not need to be heated strongly, supply line later on
- 65m² usable area
- previous owner's consumption: 15,000 kWh/year (energy efficiency class C)
- underfloor heating in kitchen, living room and bathrooms, thermostats in the basement and upper floor
- currently 2 people, later planned max. 2 children (showering yes, bathing rather rarely)
- 20-21 degrees are usually enough for us, if there are peaks of only 19 degrees on 2-5 days a year that's also okay.
Key points about the area:
Standard outdoor temperature: -10.2 °C
Annual average temperature: 11.0 °C
Altitude: 105 m
Location correction heating load: 88 %
I have now used various online tools, but get totally different sizing results (always heating + hot water):
Federal Association Heat Pump e.V. (by building type): 8.1 kW
Federal Association Heat Pump e.V. (by annual consumption): 12.9 (???) kW
German Energy Efficiency Agency: 10.62 kW
I find especially the last two strange. My house is not huge with 150m² and energy efficiency class C is not bad either. Do you have tips on how I can roughly determine the sizing before purchase (the fine tuning can then be done after a year, just that I choose the right pump now).
as already described in another thread, I want to switch to a heat pump at short notice (gas heating acting up for the second time now).
In order to find the right manufacturer/partner at all, I have dealt with the topic of sizing (not so easy, as I have only owned the house for 6 months).
Key points about the house:
- built in 2001
- 150m² living space, of which 40 are in the basement (half window) and currently do not need to be heated strongly, supply line later on
- 65m² usable area
- previous owner's consumption: 15,000 kWh/year (energy efficiency class C)
- underfloor heating in kitchen, living room and bathrooms, thermostats in the basement and upper floor
- currently 2 people, later planned max. 2 children (showering yes, bathing rather rarely)
- 20-21 degrees are usually enough for us, if there are peaks of only 19 degrees on 2-5 days a year that's also okay.
Key points about the area:
Standard outdoor temperature: -10.2 °C
Annual average temperature: 11.0 °C
Altitude: 105 m
Location correction heating load: 88 %
I have now used various online tools, but get totally different sizing results (always heating + hot water):
Federal Association Heat Pump e.V. (by building type): 8.1 kW
Federal Association Heat Pump e.V. (by annual consumption): 12.9 (???) kW
German Energy Efficiency Agency: 10.62 kW
I find especially the last two strange. My house is not huge with 150m² and energy efficiency class C is not bad either. Do you have tips on how I can roughly determine the sizing before purchase (the fine tuning can then be done after a year, just that I choose the right pump now).