Sanitary pipe installation faulty?

  • Erstellt am 2018-07-12 07:14:19

Haribobo

2018-07-12 07:14:19
  • #1
Good morning. We are currently building a prefabricated house with Allkauf Haus and have the Freetime package. On Monday, the sanitary rough installation was carried out and completed yesterday at noon. Unfortunately, all the pipes were laid where a drywall partition for the shower needs to be. Unfortunately, I was not allowed to do this beforehand because the company did not want it that way. Afterwards, I asked for advice in the Allkauf Haus Facebook group, where a member said that the pipes were laid incorrectly. His statement was: I would directly criticize the installation of the wastewater pipe. The 87-degree branches on the floor for the washbasins are completely wrong. You don't do that. The reduction for the shower is also reversed. Did a professional company do this? If so, that is sad! Can anyone confirm these statements? Then I can address this this afternoon! Best regards, Sven
 

matte

2018-07-12 07:52:28
  • #2


Wow, can you please stop with comments like that? It really doesn't help anyone. If you have nothing productive to say, please save yourself that...
 

Chilledkroete

2018-07-12 09:10:54
  • #3
For DN50, 90° branches are uncritical.

What does pose a problem, however, is the sound insulation:

Are these Skolan db drainage pipes? If so, the sound insulation which was paid for dearly is compromised by this installation: The pipe must be completely decoupled by insulation. That means even where the black nail strips are, the red insulation must be in between.

The connection for the shower is installed the wrong way around; the opening must always be on top at reductions, although this cannot always be observed everywhere...
 

Domski

2018-07-12 09:17:48
  • #4
Where do you properly secure the installation frames? On the gypsum board on the shower side, that won't work, and the wood up there only helps to keep it from tipping over. How much space do you have for your shower drywall + tiles and how much do you need?
 

Haribobo

2018-07-12 09:25:01
  • #5

Honestly, I don’t know what kind of pipes these are.. unfortunately, I have no knowledge in this area.


Where the pipes lie on the floor, a drywall wall with a thickness of 10cm must be installed. Unfortunately, this is currently not possible because the pipes and everything else are lying there and I have no space for it. The pipes lie at the boundary of 1 meter, which is exactly the width of our WEDI element.
If I put the drywall wall further to the left next to the pipes, I only have 80cm left, which is clearly too little!
 

Haribobo

2018-07-12 09:43:03
  • #6
Does anyone happen to have a picture of what the pipe in the shower should look like the right way around?
 

Similar topics
10.09.2010Does Allkauf Haus offer a full basement for 9999€?!18
14.08.2012Build a home? Land in prospect19
14.05.2016Allkauf house financing condition50
13.02.2014Shower lighting walk-in shower14
14.02.2015Floor-level shower drain with underfloor heating44
09.02.2015Floor-level shower with underfloor heating10
27.02.2016Where to lay pipes for controlled residential ventilation in the top floor ceiling21
17.10.2017Additional bathroom through the builder or just laying pipes?10
26.09.2019Is it allowed to lay KG pipes in gravel?11
02.09.2021Which shelf in the shower in the new building52
14.12.2021Realistic financial planning for KFW40 prefabricated house?38
11.11.2021How to seal pipes or entire openings11
31.05.2022Cancellation of the installation appointment at Allkauf Haus - costs or compensation?36
23.02.2024Retrofit bathtub or shower?27

Oben