Hello "scotti07". It is actually as the previous speakers have written: OSB is not very suitable. The harmful factor here is not moisture penetrating from the back (because of the "thicker" PE foil as a vapor barrier), but the humidity associated with the lack of heating in the autumn and winter months. I would design the structure similarly, i.e. possibly level the concrete pavers, lay PE foil at least 0.2 mm thick and pull it up at the edge above [OK Fußboden], set grid-like support beams with a maximum spacing of 50 cm and adjust their height. Fill the compartments in between with thermal insulation; however, for a functional insulation layer you already need 10 cm! On top, as a load-distribution layer, moisture-resistant gypsum fiber boards, at least 35 mm thick, ideally laid crosswise in this thickness (for high loads). Regards: KlaRa