Just use better insulation on the floor slab.
Our offer also included 10 cm WLG 035 under and on top of the floor slab. The heat demand calculation showed that this was not necessary for our Energy Saving Ordinance 16 compliance and planned with 14 cm WLG 035 insulation on the floor slab -> U-value of 0.24. This saved us almost €3,500, since now there were a total of 6 cm less insulation and no basement wall block was needed. However, this resulted in us having a 22 cm floor buildup and "only" 2.53 m ceiling height - but that's standard anyway.
The bottom line: The front doors were installed 1 cm too low and the screed company was cautious, which cost us another 0.5 cm, and the heating installers insisted on their Rolljet with only WLG 045. Now 2 cm of insulation were missing, which caused the U-value to go up, and I didn't want to argue with the heating company to deviate from their usual procedure. So we were faced with the problem of what to do? We talked again with the screed company, who went from 7.0 cm back to 6.5 cm and we took an aluminum foil laminated 10 cm insulation WLG 023. That cost us about €800 more than the normal WLG 035. But now we have a U-value between 0.18 and 0.19 instead of the calculated 0.24 and still saved €3,500.00 - 800.00 = €2,700.00 compared to the variant with insulation under the floor slab.
But it only works if you are flexible with the buildup height and probably not building turnkey. If you also do the insulation yourself (Anyone can really do that, but it takes some time. However, the result will be significantly better, because in my opinion a company simply doesn't have the time for the care that you put into doing it yourself), you save a big chunk of money overall.