Thanks first of all for your detailed explanation.

So basically only an internal insulation with the silicate boards would be possible.?

I have also already seen that insulation wool, for example, was installed in a stud construction with a vapor barrier/vapor retarder.
 

jens.knoedel

2024-01-06 11:13:27
  • #2
Yes, that is also possible. It must be done absolutely cleanly. If possible, such measures are avoided. Apart from that, you then need significantly more space than with the insulation boards.
 

Messerjoe

2024-01-06 12:23:24
  • #3


Yes, it is possible. I have studied a similar wall construction intensively but have not carried it out.
So I am purely sharing theoretical knowledge here:

The challenge: An interior insulation shifts the dew point exactly between the insulation and the exterior wall.

This has two important consequences that need to be dealt with:

1.) Condensation from the indoor air occurs exactly there and the wall starts to rot from the inside.

- Solution A: Install a vapor barrier on the inside of the wall.
But this has proven to be completely unusable in old buildings because even the slightest leak immediately causes massive moisture damage.

- Solution B: Build the interior insulation "vapor diffusion open and capillary active".
This allows the condensed water to simply evaporate back inside without causing damage.
This is therefore the only practicable solution in old buildings.

2.) The exterior wall is cold through and through and cannot sufficiently evaporate moisture penetrating from outside.
This also risks moisture damage, especially on weather-exposed sides.

Solution: The wall is protected against penetrating moisture by "hydrophobization".
This is a sort of coating/spray with a silicone impregnation so that rain beads off, like on shoes.
Certainly not expensive but it must be done.

Now to the insulation:
The thickness should not be sufficient to meet any energy saving ordinance or building energy law standard, because that would require at least 16 cm thickness and would leave almost no room inside (not to mention the costs).

The insulation is only supposed to make the space somewhat heatable.
I would therefore suggest 4 to 6 cm.

The construction must (very important!) be vapor diffusion open and capillary active so that moisture can be transported unhindered.

The following insulations are suitable for this:
- Heraklith wood wool boards "sauerkraut boards" (cheap and good, but not the best U-value).
- Calcium silicate boards (very good but also very expensive)
- Wood fiber boards (e.g. Steico Internal)
- Mineral fiber boards

Unfortunately, these insulation materials must be installed quite elaborately.. this is probably the biggest effort/cost factor:

- The boards must be fully glued to the exterior wall with a vapor diffusion open and capillary active material without air inclusions (e.g. applied serrated with clay base plaster and the correct technique).

- From the inside, of course, a correspondingly open finish must also be created.
This can be done with clay or lime plaster.
Cement-based plaster is of course not possible because it would block the moisture again.
Also, any interior paint must not hinder the moisture.
Maybe someone here still knows a simpler method?
Maybe a coating of the boards with clay paint is enough instead of plaster?

Regards!
Wolfgang
 

Fabian2024

2024-01-06 13:50:46
  • #4
@Wolfgang, thank you very much for your contribution, really very interesting.

what if you protect the walls from the inside with this 2K sealing slurry against penetrating moisture, that should certainly be achievable with 100 percent tightness and then install studs with wood fiber or mineral wool and then a vapor barrier?
 

Messerjoe

2024-01-06 14:31:32
  • #5

Hey Fabian!

In theory, many measures are 100% tight across the surface. But what about connections to walls, corners, windows, doors, sockets, cables, pipes, ceilings, lamps, switches? It must be 100% tight not only during construction but also remain so for many years. The smallest crack, damage, tear, detachment, drill hole, a hammered-in nail, rodent or insect damage leads to hidden condensation and rot inside the wall. So I absolutely stick to my recommendation that only a diffusion-open insulation with active capillary action through all layers is practical.
Sealing the wall with this slurry (which I do not know) would also be applied at the wrong level. Moisture must not penetrate that far into the wall if you actually want to try diffusion-tight sealing.
 

Fabian2024

2024-01-06 14:43:12
  • #6
yes, you're right, the 100% airtightness is probably just an illusion after all.

Really difficult and complex topic, I just watched the two videos you linked.
I will look into vapor diffusion open insulations that might be suitable.

Did you have a favorite in your theory?
 

Similar topics
09.10.2014Insulate attic / OSB boards11
16.05.2015Linoleum kitchen floor, click panels or roll goods16
12.01.2016Attic OSB boards measuring device15
05.05.2016Insulate the roof: flakes, panels or wool17
20.05.2016OSB panels for the attic "required", yet extra charge?33
09.08.2016Paint Gypsum boards directly???11
02.10.2016Vapor barrier vs vapor retarder21
06.02.2018The vapor barrier has a brownish position, insulation is wet27
23.06.2018XPS panels basement insulation - no bitumen layer23
26.11.2018Internal insulation with udiin, experiences28
06.05.2020Roof between-rafter insulation: Thin or thicker insulation wool?11
12.01.2021Bathroom ceiling moisture + inadequate insulation44
13.01.2021Can OSB boards be laid as flooring on carpet?10
26.02.2021(Rising?) Moisture Base / Exterior Wall11
11.09.2021Which Cat cables should be installed on the facade? Problems with moisture?29
03.06.2022Drywall on OSB boards, cracks?21
15.11.2022Keep soil away from the house with plates14
14.03.2024Installation level including insulation - influence on the insulation of the exterior wall?12
21.01.2025Remove prefabricated house walls and ceiling panels for electrical installation15

Oben