Heat pump in a partially renovated old building experiences

  • Erstellt am 2022-11-19 16:32:05

SaniererNRW123

2022-11-19 16:32:05
  • #1
For all those who are considering the purchase and (energetic) renovation of an existing property...

The day before yesterday, I commissioned a new heat pump (Pana Monoblock) in a 50-year-old attic apartment - simply connected to the old pipes.

Construction condition of the property: 60s era
Windows (almost) all new - delivery difficulties with two small dormer windows
Sloping ceilings (not many) insulated about 15 years ago with 12cm mineral wool WLG 35
Top floor ceiling insulated about 15 years ago with 12cm mineral wool (in the wooden ceiling) and newly insulated with 2x24cm mineral wool on the ceiling
Radiators as large as possible (type 33) new
Exterior walls not yet insulated (planned for next year)
The apartment below the attic is normally heated by the resident – comparable to very good basement ceiling insulation
Heat pump pipes not yet fully insulated, this will follow in the next few days

Result: at 0 degrees, the heat pump runs without short cycling with a flow temperature of 35 and a return of 30 degrees for an indoor temperature of 21-22 degrees (hydraulics not yet adjusted as calculated, valves initially out of the box).

Conclusion: The heat pump operates effectively and efficiently despite the still missing external insulation. The measures undertaken so far have also remained within a manageable scope, as many tasks could be done in-house. Energy consultant as well as engineering office on board. Not everything has to be done completely in order to break free from oil/gas. And a high-temperature heat pump is dispensable with manageable effort.
 

Proeter

2022-11-19 16:44:17
  • #2
Thank you for the exciting case report!

A few questions about it:


Wait a minute: Only in the attic apartment? So you installed a separate heating system in the attic apartment of a multi-family house, and it’s a heat pump?
This raises interesting questions:
How was the apartment heated before? Own gas heating or connection to central heating?
Where did you install the outdoor unit? This could only have been done in/on common property and would have required a resolution by the owners’ meeting? Did they just agree to that?
What was the trigger to separate a single apartment from the building’s overall energy concept?

Building condition property: 1960s
Windows (almost) all new – delivery difficulties with two small dormer windows
Roof slopes (not many) insulated about 15 years ago with 12 cm mineral wool WLG 35
top floor ceiling insulated about 15 years ago with 12 cm mineral wool (in the wooden ceiling) as well as newly insulated with 2x24 cm mineral wool on the ceiling
Radiators as large as possible (type 33) new

This point presents particular challenges in my opinion. For what heat demand is the heat pump designed?
A) For the current state (without insulation)?
B) For the future state (with insulation)?

If A: Then it is oversized with the associated disadvantages (higher investment costs, worse annual performance factor than possible)
If B: What happens if this winter gets really cold? Then it won’t be sufficient?


Impressive performance given the building fabric!
 

SaniererNRW123

2022-11-19 17:15:55
  • #3

Two-family house. And yes, currently only in the attic apartment.

Oil heating. It still runs for the ground floor. There were two circuits.

Everything belongs to me. So the community gave their ok ;)

As I said, it is a two-family house that is being renovated overall. Maybe I should have mentioned that. Mainly it was about whether a heat pump can work without a complete renovation.

Unfortunately the heat pump is oversized, but designed for the future state. A heating load of just over 4,x was calculated. The monoblocks are usually at 5. But thanks to modulation, it’s totally fine. There will be no short-cycling.

Since the heating load calculations are always based on lowest temperatures, the days (if any) could be bridged with the electric heater. Based on my own experience, I can exclude that issue. Up to -15 degrees, the heater definitely does not turn on given my circumstances.

That was what I wanted to say with the post! Insulating top and bottom + properly designing windows and heating can be a great way to get a heat pump heating system affordably.
 

Similar topics
28.11.2012Are the doors too expensive? Calculation of house costs18
07.04.2014Is new construction possible without solar and without a heat pump?20
27.05.2015Huge problem with condensation on the window34
09.06.2015Gas, heat pump, and solar for a single-family house?36
26.08.2015Cost Breakdown Heat Pump - Heat Pump with Ground Collectors23
19.05.2021Experiences with brine heat pump491
23.10.2016No heating is approved?!15
03.01.2017Preparation for photovoltaic or solar thermal with air-water heat pump18
11.04.2018Buying a piece of land with the parents - Will that work out well?22
29.05.2018Narrow plot with boundary construction - Various questions / problems26
14.09.2018Heating (Heat Pump) Incorrect, heat output too high?14
05.12.2020Gas with solar thermal? Or heat pump with photovoltaics? Consultation149
19.02.2021Combine heat pump and water-bearing fireplace60
07.06.2021Installation of heat pump/heating - before or after screed16
14.05.2022Old building apartment with gas boiler - underfloor heating now, heat pump later14
05.07.2022Renew old heating with heat pump or gas boiler and domestic hot water heat pump58
09.08.2022Decision for a heat pump29
14.01.2023Internal heat pump in the basement not possible due to groundwater?37
07.10.2023How to plan heating with a heat pump in new construction?14

Oben