Heat pump - about 60 cycles daily

  • Erstellt am 2022-02-22 10:55:10

Tx-25

2022-02-22 10:55:10
  • #1
Hello, our air-to-water heat pump Elco aerotop Split 07 cycles every 30 minutes. A hydraulic balancing has been done. In addition, I have disconnected all ERR and removed the actuators. I have carried out a thermal balancing to the best of my knowledge. However, the longest heating circuits were not fully opened in the process. I suspect that the heat pump is oversized and it then gets too warm for us. Since the heating curve is already set to the minimum. I have attached a picture where all data from the last week is recorded. From this, I have also deduced that the heat pump currently cycles every 30 minutes. In addition, the flow rate remains identical whether the pump is running or not. It must have been cycling since installation, as there are already over 10,000 cycles on the meter after 2 years. I suspect that it is all due to the settings. Therefore, I list a few settings and general data below.

146 sqm, 2 persons, single-family house, no basement, underfloor heating, ventilation system with heat recovery, photovoltaic system, insulation practically KfW 40 (without claimed subsidy).

Heat pump operation: eco plus
Flow temperature correction + 2 degrees
Pump operation modulating
Max pump PWM 100
Min pump PWM 70
Hot water 48 degrees
Set hot water temperature minimum 43 degrees Hot water is only heated at midday.
No night setback.
Silent mode set (reduction to 70% of power due to noise)
Bypass valve open, see picture
Heating curve 0.2 (0.2 to 1.0 possible)

Buffer tank:
Activation of buffer charging: off (should it be like this?)
Buffer tank hysteresis 5 degrees
Storage set temperature 40 degrees
Buffer charging type is partial charge
Buffer heating hours: 0 (for almost 2 years)
Buffer charges: 0
Buffer temperature 23°

During operation, the system shows the following values. As I have already been told here, it is strange that the hot gas has such a low temperature.

Evaporator temperature 0
Suction gas temperature 2
Hot gas temperature 28
Condenser 24
Compressor 23 Hz
Speed 625

What can be adjusted here, or is a technician inspection indispensable?

Below are my heating circuits with the lengths and current flow rates.
In parentheses are my settings from last winter. Why are the flow rates so changed (especially upstairs)? Is this due to the settings of the heat pump?

Ground floor:
WC 49 meters flow 1.0 (1.0)
Office 59 meters flow 1.3 (1.5)
Hallway 45 m flow 0.5 (0.6)
Utility room 40 m flow 0.4 (0.4)
Kitchen 84 m flow 1.0 (1.1)
Living right 89 m flow 1.9 (1.6)
Living left 106 m flow 1.7 (1.6)

Upper floor:
Bathroom 100 m flow 2.6 (1.9)
Child 1 103 m flow 1.1 (1.4)
Hallway 16 m flow 0.3 (0.6)
Bedroom 67 m flow 0 (0.5)
Dressing room 34 m flow 0 (0.6)
Child 2 88 m flow 1.5 (1.4)





 

Alessandro

2022-02-24 10:31:47
  • #2
Close the UV when you have disabled the ERR...
 

Tx-25

2022-02-24 13:24:35
  • #3
Today I turned it all the way to the right to increase the trigger pressure. I will see if that helps. I just noted down the timings.
 

Similar topics
25.01.2016Hot water only with heat pump?10
18.04.2016Heating circuits/thermostats for living/dining/kitchen with underfloor heating/heat pump35
12.01.2019New construction - Energy consumption of the heat pump / electric auxiliary heater19
25.03.2019Electricity consumption air-to-water heat pump20
12.01.2021Underfloor heating air-water heat pump. House too warm when the sun shines690
27.01.2020Properly setting the air-to-water heat pump with underfloor heating54
04.01.2022Air-water heat pump current consumption and data1439
16.10.2020CTA Aeroheat heat pump settings for improvement17
02.01.2022Hydraulic balancing air-water heat pump + efficiency circulation pump109
25.11.2021Roth heat pump single-family house setting / optimization23
04.03.2022Buy / Sell Heat Pump Privately117
26.04.2022Air-to-water heat pump without buffer storage | Heating installer refers to building energy law requirement33
31.03.2022Air-Water Heat Pump - Buffer Storage Yes or No?28
02.03.2023Heat pump for KfW55 house 148 sqm99
15.11.2022Tecalor 8.5 Air-Water Heat Pump: Warm water - not hot in the morning21
24.11.2023Heat pump: buffer tank, capacity and modulation46
05.03.2024Is a buffer tank useful in a heat pump?72

Oben