Flat collectors or gas condensing boilers

  • Erstellt am 2014-03-28 18:49:06

€uro

2014-04-22 11:15:04
  • #1
What is supposed to be supplied here, a commercial operation? 30 kW is the theoretical power output at a single operating point; how much energy is actually usable during the combustion process can be proven with a heat meter. I would not want to know the JNG of this solution.

best regards
 

fragri

2014-04-22 12:39:31
  • #2
Hello Euro,
if I burn 10kg of hardwood, I have a heating value of approximately 40kWh (4kWh/kg).
With a water content in the tiled stove of 70%, 28kWh go into the water.
Okay, ideally considered without losses!
To heat the storage (900L) by e.g. 40K, I need about 43kW. (m*CP*deltaT)
Heat quantity meters for monitoring will be installed... I can report later.
The boiler of the tiled stove is suitable as the sole heating system for buildings with a heating load up to 9kW.
I know people who additionally have no gas condensing boiler and manage with the system without freezing in winter... however, then 30 - 40kg of wood pass through the stove per day.

Regards Fragi
 

€uro

2014-04-22 14:22:21
  • #3
Correct, however this supply must also be accepted/capable of being accepted. ;-)
Actual energy or pure power supply? Pure theory, practically completely irrelevant.
Then just wait for the heat meter, the sobering will surely come! ;-)
Surely and not just pure theory? Could volume flows, the size of the heat-transferring exchanger surface, their position inside a storage tank not also play a role ;-)
I am curious!
30 kW on the water side? How is the heat distribution of the tiled stove realized on the heating side?

best regards
 

fragri

2014-04-22 15:02:14
  • #4
Hello Euro, no no... I made a mistake... not 30kW... I meant 30kW/h per burn. The tiled stove has about 10kW on the water side. The nominal heat output is 15kW. We can adjust the volume flow (flow measurement) and adjustable pump. Of course, the correct design of such a system is essential... as with other heating systems as well...
 

Similar topics
01.08.2016New lease. Heating heat meter is without power. Heating is on.11
06.02.2020Energy "concept" for old farmhouse30
03.07.2020Heat quantity meter necessary on every floor10
18.08.2022Tiled stove in combination with air-to-water heat pump experiences?13
22.02.2024Heat pumps require a lot of energy and make noise73

Oben