Correct interpretation of static calculation for garage (reinforcement...)

  • Erstellt am 2025-08-11 14:51:47

Ilchbart

2025-08-18 04:44:49
  • #1
…whereas I can't make much sense of your statement if you don't write how it is supposed to be heard correctly… Tiles will be placed on the ceiling, as it will be walkable. Maybe that's why he wrote it that way?
 

ajokr2025

2025-08-18 08:13:50
  • #2
The underside is crucial, where the statically necessary reinforcement is located. XC3 - open halls and garages - would be applicable there. So provide one centimeter more concrete cover on the underside. However, the reinforcement is still sufficient because it was calculated as one-way, but the slab rests on four sides and a Q-mat was chosen instead of an R-mat.
 

HWTIGGER

2025-08-20 14:47:41
  • #3
The answer with the Q-mats can be quite correct (not recalculated), but this only applies if the joints of the mats are designed as load-bearing joints (approx. 3 mesh overlap), however, there is no information on this.
 

Ilchbart

2025-09-12 20:11:12
  • #4
Ok, thanks. We will take your comments into consideration.
 