Just calculated the cooling
because it was not checked for this system.
However, it can be deduced from the heating capacity.
With an actual heating capacity of 35W/sqm, a cooling capacity (ΔT 8 K)
of realistically hardly more than 20W/sqm to 25W/sqm can be expected.
Nevertheless
With proper design and planning, a fantastic indoor climate is created during heating/cooling operation. In addition, daily heating operation shows that humidity and dust content in the air behave significantly more favorably.