  • Erstellt am 2021-10-10 19:13:32

Malz1902

2021-10-11 10:01:18
  • #1


Yes, I have, unfortunately no change
 

lastdrop

2021-10-11 10:17:10
  • #2
Is the pump running?

And a few more words ...
 

Malz1902

2021-10-11 10:37:13
  • #3
Yes, it is running, in the ground floor the heating circuits also warm up. I have already turned the pump up to full power, but no change in the attic either. The pump is one from Wilo.

Attached is a flow meter

 

driver55

2021-10-11 10:55:39
  • #4
please write down everything that was done, why, how, and for what reason…
 

Malz1902

2021-10-11 11:33:03
  • #5
The pipes in the attic HKV were dirty so that the set flow rate could no longer be read. I then thought I would clean them once. As a test, I did the whole thing in the basement on one, and everything worked without problems. There is flow, and the floor as well as the room get warm. I then closed the supply and return in the attic, removed and cleaned the pipes, and screwed them back on. After that, I reopened the supply and return. Then I opened the actuators again, but since then no flow has been shown in the flow meters, and the heating circuits in the attic are no longer getting warm. Attached is again a picture of how the flow meter looks in the basement and in the attic, left attic bathroom, right basement
 

borderpuschl

2021-10-11 14:30:19
  • #6
Look at the flow meter in the DG, there is a red cap missing that connects the spring inside with the white tube. Maybe that is missing and that is why.
 

Similar topics
28.01.2010House with or without a basement? - Experiences20
05.06.2010Basement made of high perforated bricks or concrete?11
18.08.2013Massive house with basement. Is our budget enough?11
08.12.2015Construction costs for KFW70 house with basement turnkey15
03.03.2012Position controlled residential ventilation in the underground basement?16
26.10.2012External perimeter insulation floor slab, basement mold risk11
09.06.2013Costs of earthworks without basement15
06.03.2013Pump noises in underfloor heating, pump in living room, noise disturbance13
19.04.2013Budget for the construction of a single-family house with a WU concrete basement27
27.05.2013Cost estimation: prefabricated house, basement, carport, single garage10
01.07.2013Additional insulation in the Ytong basement (36 cm)14
27.07.2013Average construction time for a semi-detached house with a basement11
29.07.2019How does my heating system with solar thermal work?42
23.05.2019Purchase of single-family house - Water is leaking into the basement21
10.08.2019Single or two-family house with a hole in the basement11
19.02.2020Discoloration of heating water (only the supply line)20
14.07.2020Backflow valve with pump or without12
22.07.2021Cistern for garden irrigation - Which pump?69
20.03.2021Basement underfloor heating or low-temperature radiators22
25.04.2023Heat pump LWZ 403 Sol high supply + return in solar thermal. Underfloor heating is malfunctioning...13

Oben