Heat pump, Google and oil-based heating installers are an explosive mix, where in the end a lot of crap can hit the fan.
There is no heat protection certificate yet because I have done everything myself so far and without funding applications I didn’t need one.
According to the Building Energy Act 2020, the heat protection certificate is part of the building application. Someone must have calculated something. Whether it corresponds to reality is another matter.
An acquaintance took a bit more for his single-family house, also extra for hot water, because it is often problematic, he says
More helps more has always been the saying with oil and gas boilers. 20% more power is no problem, just costs about 10% more, but during operation you hardly notice it. Heat pumps, on the other hand, that are too big, always deliver enough heat – but above 0°C quickly go into short cycling mode because they cannot modulate down that far. It’s not the bare kW number that matters here, but also the lower performance limit at moderate outside temperatures (heat pumps do not have their lowest possible output at higher (0°C-10°C) outside temperatures). It is not necessarily harmful to choose one size larger if the lower modulation limit stays the same. In general, no one needs more than 8 kW in a new single-family home – if yes, then the hot water tank is too small, or the rain shower is supposed to run at the same time as the bathtub, after the 3 kids have come back from sports and showered everything empty. That has to be taken into account in the planning.
My building materials dealer has already entered it into his program once and said even 30 kW.
I didn’t know they also do HVAC planning now.
Input mask – field1: "Area", field2: "Number of residential units", field3: "Year built"?
Output: 30 kW
Is 14 kW really enough there? And which one would you recommend then?
I don’t know. Keyword: room-by-room heat load calculation and domestic hot water demand calculation. Software: Hottgentroth, BKI Energieplaner or others.
Heating demand according to Google on several platforms:
Maybe Chat GPT knows more.
There is no fixed heating demand for KfW standards or their energy classes, nor for GEG2020.
The allowable maximum heating demand per year for new buildings must not exceed that of the respective reference building.
The reference building is a virtual house of the same volume with the same component areas (windows, roof, wall, floor) built from the respective valid standard components and with a standard heating system according to the Building Energy Act 2020 with correspondingly improved values according to KfWxx.
So you can build a 3m wide 20m long tube-shaped building with one floor and a complete glass facade on the north side with very high heating demand and still fulfill GEG2020. Or you build a cube with minimal windows, all facing south, and also have the building standard according to the Building Energy Act 2020 – but significantly less heating demand.
The larger the house is, the lower the heat demand per m² usually is, unless it is a tube.
For domestic hot water, a surcharge of about 20% then results in about 22 kW
Where does that come from? Flat rate? Why? Makes no sense. If the heat load is greater than the peak load required for the used buffer/ hot water tank and the heat load calculation already includes standby times for heat pump tariffs and hot water preparation, you don’t need a surcharge for hot water. If yes, -> change tank size.
My acquaintance heating installer roughly calculated a 24 kW boiler for oil or gas heating with my data.
Oil/gas heating → totally different story in sizing, because it doesn’t matter at all if it is 100% too large.
For 4 apartments I would install a small heat pump with hot water thermal storage in each apartment.
I have little to say about the rant, but the suggestion is not bad at all, especially if no separate HVAC planning is to be done. The problem here is that the smallest heat pumps on the market usually have 5 kW nominal output and about 2 kW minimum output and then all are too large because the heat load of the respective individual apartment is too small.
has already written how he solved it. Just as I suggested – calculate the heat load, size heat pump and suitable buffer storage with fresh water station accordingly. A flat rate won’t work.