Hello forum,
the penetrating moisture can only have a few causes:
- Tap water: test with water meter negative, theoretically there could still be a leak before the water meter.
- Backflow of wastewater: wastewater always smells, so probably negative, the pending sewer inspection will bring clarity.
- Heating leak: if the pressure in the heating system remains constant, it is tight. I assume this point has already been considered - negative
- Condensation moisture: the dew point is not undershot - negative
- Faulty roof drainage: the moisture flows evenly in all weather - negative
- Penetrating moisture from the ground: even if the building structure was constructed as a [Weiße Wanne], the tightness is not proven. Penetrating moisture can flow in evenly.
If the sewer inspection brings nothing (which I assume), in my opinion only penetrating moisture from the ground remains. Otherwise, the even flowing in of the water cannot be explained.
The cause is therefore probably somewhere in the building structure, or in the area of earth-contacting wall penetrations (electricity, water, wastewater pipes, etc.).
A leaking wall penetration can be repaired quite easily after precise localization.
In case of defects in the building structure itself, you will probably face an extensive renovation.
Good luck and best regards
Kristof
the penetrating moisture can only have a few causes:
- Tap water: test with water meter negative, theoretically there could still be a leak before the water meter.
- Backflow of wastewater: wastewater always smells, so probably negative, the pending sewer inspection will bring clarity.
- Heating leak: if the pressure in the heating system remains constant, it is tight. I assume this point has already been considered - negative
- Condensation moisture: the dew point is not undershot - negative
- Faulty roof drainage: the moisture flows evenly in all weather - negative
- Penetrating moisture from the ground: even if the building structure was constructed as a [Weiße Wanne], the tightness is not proven. Penetrating moisture can flow in evenly.
If the sewer inspection brings nothing (which I assume), in my opinion only penetrating moisture from the ground remains. Otherwise, the even flowing in of the water cannot be explained.
The cause is therefore probably somewhere in the building structure, or in the area of earth-contacting wall penetrations (electricity, water, wastewater pipes, etc.).
A leaking wall penetration can be repaired quite easily after precise localization.
In case of defects in the building structure itself, you will probably face an extensive renovation.
Good luck and best regards