Volume flow rate specification of controlled residential ventilation for heating load calculation

  • Erstellt am 2022-10-14 01:44:29

i_b_n_a_n

2022-10-14 11:21:36
  • #1
well, decentralized kWh in push-pull operation like this (that's how I understood it as a layman) > heat storage component is heated on one side by outgoing air, on the other side the incoming air is reheated by this preheated component. but everything is still far from the efficiency of a rotary heat exchanger in a central controlled residential ventilation system. the whole thing preferably in one device (in/out also in quick succession). my brother-in-law (HVAC planner!) installed it in a rental apartment - horribly loud (mathematically good ;-) )
 

JaiBee07

2022-10-14 11:36:28
  • #2
Sorry, I have to follow up because I still don’t quite understand the values and I now need to provide the "Heizlastberechner" with something final and as accurate as possible.

According to the manufacturer’s datasheet, the fan has
Airflow in ventilation mode (m3/h): Level 1=15; Level 2=30; Level 3=50
Airflow in regeneration mode (m3/h): Level 1= 8; Level 2=15; Level 3=25

So apparently in regeneration mode, half the airflow is assumed because the fan changes its rotation direction and then runs 50% of the time in the other direction. Apparently, only the exhaust or only the supply air is considered.

But I have 2 fans, and if, for example, you consider the supply air, the 2nd fan will be working on supply air during the time when the 1st fan is working on exhaust air. So I would have double the supply air than what is stated under regeneration mode.

So, based on this information, I would have to specify a volume flow of 30m3/h at level 2, right?
 

JaiBee07

2022-10-14 11:40:16
  • #3


Yes, exactly like that. With the reversing devices, just one after the other. First, the warm room air drawn in preheats the ceramic. Then, when the cold outside air is drawn in, it is preheated again by the stored energy from the ceramic. Since the stored heat only lasts for a certain time, this process has to be repeated continuously.
 

WilderSueden

2022-10-14 11:49:30
  • #4
Yes, in this case you get 30cbm/h because two fans are in regeneration mode. And wire them so that they are not both doing the same thing.
 

JaiBee07

2022-10-14 11:53:16
  • #5


Yes, the system does that automatically if configured accordingly. One is the master and the other always adjusts the rotation direction opposite to the master.
 

Similar topics
09.09.2015Living area with step10
03.10.2016Exhaust air and supply air one above the other?22
27.01.2017Exhaust air vs. recirculated air in a controlled residential ventilation system32
13.02.2017Number of supply and exhaust airflows in residential ventilation11
20.04.2017Controlled residential ventilation: place supply air in bedrooms in the wall.23
05.05.2017Central Controlled Residential Ventilation: Supply and Exhaust Air, Door Bottom Gap30
19.01.2018Controlled residential ventilation system - decision support31
10.06.2019Controlled residential ventilation - Is stage 7 out of 9 an acceptable design?22
09.01.2018Exhaust air in the bedroom - supply air in the storage room24
12.12.2018Terrace level with the ground? Or with a step?12
04.02.2019Level between living room and kitchen-dining area14
17.02.2020Open kitchen: exhaust or recirculation in controlled residential ventilation & KfW5540
15.10.2020Controlled residential ventilation: positioning of supply and exhaust air in my designs44
23.06.2021Controlled residential ventilation - Planning the positions for supply air / exhaust air60
19.05.2021Should the path to the garage be made "slanting" or with a small "step"?!?17
21.05.2021Step from the living room to the terrace?13
02.06.2021Controlled residential ventilation supply air in the living area near the sofa19
17.08.2021House costs per KFW level per m²32
19.11.2021Extractor hood: recirculation or exhaust air for KFW55?27
29.03.2024Lowering the KfW level - impact on loan amount?13

Oben