Hello everyone,
we are currently having a Luxhaus (timber frame construction) built and had our shell inspection last week. An independent master carpenter pointed out to me that the staples used to attach the vapor retarder (I assume it is a vapor retarder and not a vapor barrier, since it is a PVC foil) at the transition to the attic should have been sealed with sealing tape for airtightness. (currently, they are not).
By the way: The attic of the truss roof is located outside the insulated area.
Luxhaus is quite relaxed about this and referred us to the blower door test. If there were any leaks, they would be detected during the blower door test. Sealing the staples would make them no longer competitive.
After some research on the blower door test, I came to the conclusion that it is not necessarily a conclusive confirmation that there are no leaks. On the one hand, because this test can be carried out by anyone without special qualifications, and on the other hand, meeting the KfW limits is no guarantee that there are no leaks due to construction defects.
How do you see it?
Best regards,
Anton

we are currently having a Luxhaus (timber frame construction) built and had our shell inspection last week. An independent master carpenter pointed out to me that the staples used to attach the vapor retarder (I assume it is a vapor retarder and not a vapor barrier, since it is a PVC foil) at the transition to the attic should have been sealed with sealing tape for airtightness. (currently, they are not).
By the way: The attic of the truss roof is located outside the insulated area.
Luxhaus is quite relaxed about this and referred us to the blower door test. If there were any leaks, they would be detected during the blower door test. Sealing the staples would make them no longer competitive.
After some research on the blower door test, I came to the conclusion that it is not necessarily a conclusive confirmation that there are no leaks. On the one hand, because this test can be carried out by anyone without special qualifications, and on the other hand, meeting the KfW limits is no guarantee that there are no leaks due to construction defects.
How do you see it?
Best regards,
Anton