Properly setting the air-to-water heat pump with underfloor heating

  • Erstellt am 2019-12-15 16:52:05

M4rvin

2019-12-20 19:05:18
  • #1
No idea what this is... I had hoped you would get more flow when you turn it on. Unfortunately, I didn't find any fuse, I'll set it to 0! Thanks!
 

guckuck2

2019-12-20 19:10:58
  • #2
Looks like a differential pressure bypass valve.
 

Daniel-Sp

2019-12-20 19:11:56
  • #3
If it is a [Überströmventil], it opens earlier when you turn it further. Try closing it step by step and observe the flow in the tubes. Maybe you can get a little more flow. Remember the current setting, then you can always reset it. I was able to increase the flow from 1200l/h to over 1800l/h by closing the [Überströmventil] on my system...
 

seat88

2019-12-20 20:49:51
  • #4
If you had simply called the local heating technician, he would have fixed the problem in an hour and for 44.72 euros. That would have saved you the adjusting, rearranging, and trying out for the fifth day in a row....
 

tomtom79

2019-12-20 20:58:01
  • #5
Haha that was good, never.
 

M4rvin

2019-12-20 21:56:26
  • #6
I already called, my appointment is on 01/10. But I think if you roughly set it in the right direction beforehand, it will be easier for the technician! By closing the valve, do you mean setting it to lower pressure?
 