Measurement values natural cooling heat pump

  • Erstellt am 2012-07-26 13:28:59

merlin667

2013-07-29 09:16:12
  • #1
if you don't trust your heating engineer:
Operating instructions
If that doesn't help, call the manufacturer.
If someone here has experience with your heat pump, they can still help you, as the controls are very manufacturer-specific.
 

Slevin

2013-07-29 09:17:44
  • #2
The instruction manual is not very informative on the topic, response from the manufacturer is still pending.
 

Slevin

2013-07-29 09:22:00
  • #3
The brine circuit is definitely in motion, I just turned on the cooling. The source was at around 20°C, shortly before there was domestic hot water operation and it dropped to 11°C within about a minute. Supply/return stabilized at 24.2°. Outside temperature 21°C inside 23°C.
 

Slevin

2013-07-29 09:23:51
  • #4
Strangely, the temperature of the suction line rises from 33°C now to 40°C
 

merlin667

2013-07-29 09:55:53
  • #5
That means the brine circuit is running, do you happen to have supply and return temperature sensors there as well, is the heating circuit still running? Have you checked in winter operation if you have a difference between the heating supply and return? What is the room temperature now? Where was the supply/return temperature before switching on? What must not be overlooked: cooling 1 liter of water per second by 1° requires about 4.2 kW cooling capacity (P = V x t x c). No idea what heating capacity you have, but with 8 kW heating capacity and a 5° difference between supply and return, about 1400 l/h come out. That means 0.5° between supply and return would be 0.8 kW or 1° would be 1.6 kW cooling capacity. To me, that means you should always see a little something.
 

Slevin

2013-07-29 10:01:28
  • #6
Heating operation runs great, usually around 28°C supply and 25 return. I don't know about the source on/off in winter, with the source temperature there is a difference of at least 0.3°C between inlet and outlet. The source temperature hardly changes in cooling operation.
 

Similar topics
27.11.2017Ventilation system with heat recovery, installation location temperature11
29.07.2019How does my heating system with solar thermal work?42
24.12.2017Correct temperature for a 300-liter hot water tank?17
19.02.2020Discoloration of heating water (only the supply line)20
22.10.2020Gas heating capacity selection 20kW instead of 14kW29
11.12.2021Wall heaters do not reach the desired temperature53
25.04.2023Heat pump LWZ 403 Sol high supply + return in solar thermal. Underfloor heating is malfunctioning...13

Oben