Is an extra circuit / residual current device really necessary for the office?

  • Erstellt am 2020-06-09 17:23:46

kati1337

2020-06-09 17:23:46
  • #1
Hi!

I need to ask again because we know so little about electrical stuff. I don’t know if we’re being led around by our electrical company, or if the additional costs are necessary and justified.

We have planned an office where we want to set up 2 gaming PCs. We originally planned 18 sockets there (just to have enough), but are now reducing this to 8. However, for each PC we will probably need a multi-socket power strip (1 computer, 2 monitors, possibly some small stuff like a label printer or so).

The electrician says:

    [*]We need an extra circuit for the office 150€
    [*]an extra RCD 115€
    [*]and because we get an additional circuit and RCD for it, also a bigger distribution board – 490€

All prices are net.
Can it really be that we have such a chain of costs because of this? Is this necessary?
He says if we don’t do this (with the circuit / RCD) we can save the bigger distribution board, but then we wouldn’t be allowed to use multi-socket power strips there (would be a big fire risk).

I’m surprised because we’ve been running exactly this setup in our current house (30 years old, only one RCD for everything) for almost 10 years without any problems (or fires). Are we risking our lives every day for years here, or is the truth somewhere in between?
I’m not sure right now what to do here.
 

Mycraft

2020-06-09 17:29:08
  • #2
Of course, it depends on the power consumption of the technology. A gaming PC is not the same as a gaming PC

But the colleague is trying to protect you from damage and not rip you off or anything. What he says is probably true.

Actually, in my opinion, the electrical installations are planned way too tightly in new buildings.

No one from a distance can say how things currently look for you and whether you risk a fire daily.

I would do it. Safety comes first.
 

kati1337

2020-06-09 17:37:14
  • #3


Both gaming PCs each currently have 600-700W power supplies. The monitors consume significantly less (obviously). The PCs are clearly the main consumers. There is also a printer, but it is turned off most of the time.
 

Flocko1

2020-06-09 17:38:39
  • #4
My knowledge based on the VDE is that sockets must always be protected by an RCD.

Edit:
here is an excerpt from the VDE:
VDE 0100-410 from June 2007 states that newly installed sockets with a rated current up to 20 amperes in indoor areas must be equipped with residual current devices (RCDs). However, this regulation does not always apply – there are exceptions.
According to DIN VDE 0100-410 (VDE 0100-410):2007-06, newly installed sockets up to 20 A rated current/current rating, which are installed indoors, must be protected by residual current devices (RCD) with a rated residual operating current ≤ 30mA.
 

Tarnari

2020-06-09 17:39:05
  • #5
Since I myself like to game, although much less than before, I would also like to add the following. A decent gaming rig costs quite a bit and is upgraded or replaced at least every once in a blue moon. One could now say, with the proposed equipment you are investing in an already not cheap hobby.
 

kati1337

2020-06-09 17:45:37
  • #6


They are indeed. We are building new, we are already getting 2 RCDs anyway.
The electrician wants to install an additional circuit (?) (feeder distribution) and a third RCD just for the office.
My question is whether this is necessary.



I like to invest in the (admittedly not cheap) gaming equipment. But only if the investment is necessary. That’s why I’m asking here whether this really makes sense or not. I don’t want to save in the wrong place, but I would like opinions from others on whether what the electrician suggests is necessary. After all, we can’t be the only ones gaming together, right?
 

Similar topics
24.12.2015Electrical planning - sockets88
13.04.2016Electrical planning: Where to install sockets, LED and LAN outlets?19
21.03.2019How many power outlets are behind the TV?78
12.05.2017Is an advance payment to an electrician lawful?23
15.08.2017Sockets directly under light switches? Pros, cons?17
12.09.2019Electricity in garage: fuse box, circuit, sockets21
01.08.2019Trouble with the electrician / tolerance range?!42
16.07.2019Sockets and light switches are not connected in parallel22
04.08.2019Sockets: Always prepare sets of 5? What is the best way?25
20.02.2020What does the electrician do during the shell construction phase?19
13.10.2020Planning sockets and burn sites36
01.03.2021Retrofit child safety socket / touch protection22
09.04.2021Switchable sockets / Ideas and tips18
27.12.2022Wiring sockets, switches30