So, the soil doesn't look too bad at first. Have there been any dynamic probing tests conducted? From the documents, I gather that strip foundations are planned?
I'll give a brief assessment and what I would have written...
Since there are silt components in the sandy soil up to 1.5 m below the [GOK], this is not frost-resistant. The geotechnical engineer should have specified the frost action zone and the frost-proof foundation depth in their report.
Frost protection can be ensured by:
1. A frost-proof structure. This means excavation and installation of F1 material up to 1.0 m below [GOK] (1 m is only assumed, [GOK] is the new planned ground surface level).
2. Frost skirts up to 1.0 m below [GOK] (then non-frost-resistant but still well-compacted material can be used).
3. Strip foundations up to 1.0 m below [GOK].
Building waterproofing:
Here, either a perimeter drain with damp-proofing against soil moisture or a waterproof concrete slab against pressurized water is recommended. Since I do not know the site conditions, I will just rely on the statement. I would clearly tend to recommend drainage here, as it is cheaper to implement if allowed. Theoretically, infiltration of rainwater into the sands should also be possible... but that is another topic.
Foundation:
The topsoil must be removed, that is clear. Nothing more was demanded by the geotechnical engineer.
1. If you want to found without foundations (frost skirts/strips), you must ensure the frost-proof structure up to your planned foundation base. However you manage that (more filling, more excavation, shifting the foundation level, etc.)
2. Frost skirts serve only against frost and are not responsible for load transfer. Here, after the topsoil is removed, well-compacting material can theoretically be backfilled.
3. Loads are transferred through the strip foundations (the report should have details here) into the ground. The structural engineer calculates the number, location, and dimensions of the foundations. The topsoil must be removed and the "void" up to the concrete slab (up to the insulation) must be backfilled. Here too, I would use compactable material (does not have to be F1), although the slab itself does not carry loads.
Soil analysis:
I would wait with an analysis. This concerns topsoil that should actually be characterized according to [BBodSchV]. But who knows what the earthworks contractor intends with it. So if the disposal route is clarified, then ask the earthworks contractor which analysis they need and have exactly that done.
Regards