Interpretation of Earth Drilling Experiences

  • Erstellt am 2023-11-03 22:52:35

JaiBee07

2023-11-03 22:52:35
  • #1
Hello everyone,

I received an offer for the ground drilling today and need some support with the evaluation of the data.

The following was provided to me in a document:

Your heat pump: Nibe Systemtechnik GmbH: NIBE F1255-6
planned heating capacity 6 kW
annual heating energy demand 6,450 kWh
annual domestic hot water energy demand 4,000 kWh
annual heating profile Standard new build load profile

YOUR GEOLOGICAL CONDITIONS

undisturbed site-specific soil temperature 9.7 °C
specific thermal conductivity of the geological layers 2.2 W/(m*K)

Number of drillings 2
Depth per drilling 60m
Flow type Turbulent
Probe type Single U-probe 40

Energy output: Your drilling field generates for you (in megawatt hours) p.a. 8.2 MWh

According to the calculation by the engineering office, my house has a heating load of 4297W (without domestic hot water).
There is an error in the planned heat pump; it should be the Nibe S1255-6-PC, not the F1255-6. However, I think this makes no difference here.

Is it normal to simply size the probes according to the maximum heating capacity of the heat pump (6 kW)?
I don't understand the two values specified for annual heating energy demand and for domestic hot water energy demand. Why is 6450 kWh used now?
A domestic hot water energy demand of 4000 kWh for a 3-person household also seems extremely high to me, doesn't it?
Can someone shed some light on this?

In the end, I am surprised by the 2 drillings and the associated estimated costs (almost €14,000).
I had actually hoped to manage with 1 drilling due to the rather low heating load. According to the diagram for the state of Berlin, the soil in my area should provide about 35W/m.

Best regards
 

guckuck2

2023-11-04 10:29:35
  • #2
4000kWh for hot water is not much. Remember, they are talking about heat, not electricity.

But yes, I would insist on a borehole, a double U probe. It shouldn't be more than 100m (and even if it is, you simply go deeper than 100m instead of installing two probes).
 

JaiBee07

2023-11-04 12:14:39
  • #3
But online I find surcharges of 600-800kWh per person for hot water. For 3 people, that would rather be in the range of 1800 to 2400kWh. Here almost double is indicated. On other sites, however, it says that some do not include any surcharge here at all, because the standards for heating load calculation already include so much reserve (e.g. solar gains) that it is not necessary. Besides, the heating never does both, but prioritizes hot water preparation.

But I first want to understand the numbers so that I can then argue with them. Does anyone have an idea where the heating energy demand of 6450kWh p.a. is derived from?

PS: Drilling over 100m apparently is not possible, then you are in the mining area and need completely different approvals that no one will give you.
 

guckuck2

2023-11-04 18:35:34
  • #4
From 100m on, the application process is more extensive, yes, but of course it's possible. We have done it too. It's just significantly cheaper.
 

i_b_n_a_n

2023-11-05 17:13:42
  • #5
I can confirm, I also have "only" a 110m borehole for the house. An Alpha Innotec WZSV 62K3M (1.25 - 5.95 kW incl. PC) was installed.
 

JaiBee07

2023-11-06 10:10:16
  • #6
Is my assumption even correct that a borehole with 120m would be more cost-effective than 2 boreholes of 60m each? (I am aware that you probably cannot simply calculate this based on the performance of the ground probe). Are 2 boreholes in any way advantageous?
 

Similar topics
26.08.2015Cost Breakdown Heat Pump - Heat Pump with Ground Collectors23
19.05.2021Experiences with brine heat pump491
25.01.2016Hot water only with heat pump?10
07.02.2016Combination of air-water heat pump + solar thermal + stove or only stove and air-water heat pump13
05.02.2020LW Heat Pump Alpha Innotec LWDV with 12KW26
14.12.2020Ice formation brine pipe heat pump78
04.01.2022Air-water heat pump current consumption and data1439
02.01.2021City villa floor plan 180m², basement, 3 children - Your opinions on this?51
06.03.2023Alpha Innotec heat pump failure23
15.11.2022Tecalor 8.5 Air-Water Heat Pump: Warm water - not hot in the morning21
25.02.2023Is my heat pump from alpha innotec good?10
18.09.2023Optimization of heat pump LWD 70A with photovoltaics16
13.02.2024Heat pump is not compatible with a water-bearing fireplace144

Oben