Elias_dee
2022-04-24 10:40:13
- #1
Good morning,
we are building a turnkey single-family house for 2 people starting from October 2022, the framework conditions are:
- Air-to-water heat pump
- Possibly photovoltaic system (not yet certain)
- Central ventilation system with heat recovery
- House will be occupied by 2 people
- Ground floor + upper floor + basement (partly used as living space)
- No KFW, standard, construction according to the Building Energy Act, 36.5 cm bricks
The general contractor sent me the calculation and planned circuits from the heating installer, see attachment. Calculated based on 205 m² living space x 0.035 -> 7.17 kW + 0.8 kW hot water --> 8 kW
Safety factor 1.2 --> 9.6 kW
The heating installer offered the following via the general contractor based on this planning:
- Weishaupt Biblock WBB 12-A-RMD-AI
- Combination storage tank WKS 300/100LE / Unit / Bloc / C, 300 liter domestic hot water tank and 100 liter buffer tank
- 12 room thermostats
Now I have already read a bit here and elsewhere and understood that individual room control is nonsense and the circuits should rather be designed for the corresponding temperature in advance (at least that's how I understood it, please correct me if I'm wrong).
Also, opinions seem to be very divided on the subject of buffer tanks, but the tendency is rather: unnecessary. Honestly, I have not quite understood why yet. I keep reading that such a design quickly wears out an air-to-water heat pump and leads to high electricity consumption. The safety factor also seems to be set rather high by the heating installer.
Without having real expertise in this, I would prefer not to start a discussion with the heating installer. Could you advise me on how the concept for our single-family house can be better designed?
Thank you very much in advance!
Best regards, Elias

we are building a turnkey single-family house for 2 people starting from October 2022, the framework conditions are:
- Air-to-water heat pump
- Possibly photovoltaic system (not yet certain)
- Central ventilation system with heat recovery
- House will be occupied by 2 people
- Ground floor + upper floor + basement (partly used as living space)
- No KFW, standard, construction according to the Building Energy Act, 36.5 cm bricks
The general contractor sent me the calculation and planned circuits from the heating installer, see attachment. Calculated based on 205 m² living space x 0.035 -> 7.17 kW + 0.8 kW hot water --> 8 kW
Safety factor 1.2 --> 9.6 kW
The heating installer offered the following via the general contractor based on this planning:
- Weishaupt Biblock WBB 12-A-RMD-AI
- Combination storage tank WKS 300/100LE / Unit / Bloc / C, 300 liter domestic hot water tank and 100 liter buffer tank
- 12 room thermostats
Now I have already read a bit here and elsewhere and understood that individual room control is nonsense and the circuits should rather be designed for the corresponding temperature in advance (at least that's how I understood it, please correct me if I'm wrong).
Also, opinions seem to be very divided on the subject of buffer tanks, but the tendency is rather: unnecessary. Honestly, I have not quite understood why yet. I keep reading that such a design quickly wears out an air-to-water heat pump and leads to high electricity consumption. The safety factor also seems to be set rather high by the heating installer.
Without having real expertise in this, I would prefer not to start a discussion with the heating installer. Could you advise me on how the concept for our single-family house can be better designed?
Thank you very much in advance!
Best regards, Elias