Design of underfloor heating for KFW 55 house with ventilation system

  • Erstellt am 2023-02-17 16:29:34

KarstenausNRW

2023-02-20 13:25:46
  • #1
Just a dumb question. How do you come up with 6/12/18 cm installation spacing? No tack board or studded board is designed for such distances. People always talk about 5, (7.5), 10, 15 cm. When I read such distances and then see that a large part is supposed to be installed with 18 cm, it makes me sick. Almost 20 cm was state of the art 30 years ago, but not anymore today. Nowadays, you should basically plan with 10 cm or, where necessary, 5 cm (bathrooms). That costs a minimal effort (+ material) more, but leads a) to significantly lower supply temperatures, which feels better and is more economical and b) thus reasonably planned 22 degrees in living rooms are comfortably achievable. You discuss these topics with a qualified planner. Wrong: A qualified planner asks about your wishes. In your case, the cheapest solution for the construction contractor is installed – it will get warm, but it’s like Dacia to Mercedes. Both get you from a to b but with different comfort levels (only the price difference in cars is significantly higher).
 

dream2023

2023-02-20 13:32:26
  • #2


I don’t know. Apparently, this stud plate is exactly dimensioned like that. The site manager said at least I can’t just install a different system than the one intended for the heating. That the laying distances are indeed unusual, I’ve heard several times now.
 

dream2023

2023-02-20 13:34:30
  • #3


A controlled residential ventilation system is being installed.
The site management was really unhappy about my skepticism. I don’t think they are open to major changes.
 

Pacmansh

2023-02-20 13:42:53
  • #4
They are used to that and you just have to make yourself a bit unpopular. They know their characters and know who does somewhat better work and who doesn't. Therefore, he also knows that rework is necessary when the buyer/client thinks things through themselves.
 

hanse987

2023-02-20 13:56:19
  • #5
If I see it correctly, a flow temperature of 35 degrees is being calculated. That would be too high for me. I would have it calculated with a flow temperature of 30 degrees.
 

Pacmansh

2023-02-20 14:15:21
  • #6
That's all well and good, but what is supposed to come out of it? According to calculations, he already has an undercoverage at 35 degrees in the bathroom. If you now calculate with 30 degrees, the undercoverage will only increase and then the OP either has to accept that it will only be 21 degrees warm in the bathroom or the plumber won't install it for him.
 