Connection insulation from basement wall to floor slab

  • Erstellt am 2016-07-13 00:35:34

cumpa

2016-07-13 00:35:34
  • #1
Hello. Our floor slab is insulated from below with 6cm. The walls of our [Weissen Wanne] are insulated with 14cm. The insulation of the floor slab sticks out a bit on the ground and the wall insulation was roughly placed on it. However, in some places there is a wide gap / between the insulation of the floor slab and the edge of the wall panel so that you can put your hand through. (Thermal bridge)? Is that normal? The pit will be backfilled tomorrow. Attached photos
 

wpic

2016-07-13 10:05:54
  • #2
No, normally the perimeter insulation boards should be installed/adhered without gaps and thermal bridges. The gap must of course be closed. In addition, the boards must stand upright at the bottom so they are not torn off when backfilling. Simply foaming will not be sufficient there. The gap must be filled as accurately as possible with an insulation strip. For foaming smaller joints/defects, only PU perimeter filling foams approved for this purpose are to be used, however not in the case of "pressing water" load, which may apply in your case if you have received a [Wesse Wanne]. The pit cannot be backfilled in this way. Furthermore, a stud protection sheet must be placed in front of the insulation as a backfill protection.
 

cumpa

2016-07-13 23:41:25
  • #3
Hello Wpic... a system PU assembly foam from Lohr Element was used to seal the joints. We do not have pressing water, but rather temporarily accumulating seepage water. After foaming the joints, then dimple sheets were applied....
 

SV-Bau01

2017-04-04 20:27:52
  • #4
The sealing of the floor slab up to the wall does not have to be done, as [Weiße Wanne] has certainly been agreed upon. However, the insulation should be laid up to the bottom and on the ledge of the floor slab to reduce thermal bridges. And hope that everything remains sealed. The rest is already stated above.
Best regards
 

Similar topics
31.05.2015Wastewater pipe concreted in the floor slab at the wrong location29
26.10.2012External perimeter insulation floor slab, basement mold risk11
01.07.2013Additional insulation in the Ytong basement (36 cm)14
12.08.2015Is insulation worth it beyond the new construction standard?34
24.08.2021Slope position, basement open at the front, bathtub31
11.09.2016Base plate - construction/insulation etc. - experiences please!10
11.10.2017Sealing on Styrodur insulation?14
13.09.2016Insulation under the floor slab EPS or XPS?12
29.07.2018Perimeter insulation under the floor slab and still XPS under the screed?28
06.10.2016Base plate with defects?22
27.11.2016Double insulation below and above the floor slab?10
06.10.2019Base plate with concrete core activation. What is your opinion?46
26.02.2018Insulation under reinforced concrete floor slab KFW5520
20.06.2018The basement should become warmer - underfloor heating, insulation?11
07.01.2019House with slab foundation on a slope52
09.02.2019Ground slab with strip foundation and frost skirt23
01.07.2019KFW 55 - Insulation under the floor slab37
02.02.2020Insulation under the floor slab - Is it sensible? Experiences39
20.01.2020Bitumen welding membrane on ground slab19
29.04.2025Insulation of the ground slab in the basement with thermal stone12

Oben